Does the new system condition all of the air, or does it run and mix in recycled air as needed for temperature? Do you know what the Freon temperature is at the evaporator, and what are the air temperatures (in/out)?High Relative Humidity is my biggest problem now in the operating rooms… 20-60% is my range and no surgery can start outside this range.
My readings with the new HVAC are consistently 57-60%
Contractor has been trying all kinds of things with little success.
68F is ideal operating room temp so warming the room not an option.
The old system was always plus or minus 50% RH
View attachment 3817922
Might be a Freon fill issue, or that the new air flow velocity that is too high, or the controller isn't getting the right inputs and not calling for enough cooling, or possibly poor drainage. One way or another, your evaporator is either not getting cold enough, or the air flow is too high, and the air is not getting cold enough. With more modern refrigerants, (non-R22), similar cooling capacities don't always get the dehumidification that one might be used to. Evaporators often get sized for efficiency these days, and that often leads to a lack of humidity control. Sometimes the "simple" way is a separate dehumidifying system.
I've been on this sort of snipe hunt more times than I like to recall.
All the best,
Peter