"in effect it was only getting 120V"
In the interest of even more ejumication, you didn't even have 120 volts if it was wired correctly - 240 volt wired plugs (3 prong) have two hot wires 120 volts and 180 degrees out of phase, and an equipment GROUND - no neutral. So even though you had 120 volts at one contact, there was no return path so no current could flow.
An equipment ground is supposed to be ONLY connected to the chassis/frame of the equipment so an internal wiring problem cannot cause the outer parts of the device to be live.
Newer stuff, especially with a motor of some type and/or electronics, uses a 4 prong plug - it has the same 3 wires as a 3 prong, with an added neutral so 120 volt power can be had and still meet code. On those units, the neutral is only connected as a return for any 120 volt components, and the ground is only connected to the frame.
I know it seems weird at first, but even though BOTH the ground and neutral attach to the same buss bar in your panel, the ground is NEVER supposed to carry current unless there is a problem - but a neutral will carry just as much current as the hot wire since it is the return.
HTH... Steve
Good explanation Steve.:thumbsup: