CobyRupert
Super Member
Does turning one of the two breakers off have any effect on the other one?? It could be that a shared ground (grounded/neutral) wire has a bad connection.
This is what I 1'st suspected, except:
- You would tend to get an overvoltage on one leg (L1), and an undervoltage on the other (L2) that adds up to 220/240 volts. (- although I suppose, a loose connection could then cut this to the 206V (108V + 98V) that the OP measured.
- Hopefully his house doesn't have multiwire ciruits that share a neutral run from (2) single pole breakers (located on opposite sides of the panel.) This would be unlikely.
I'd still do the test, it can't hurt.
Check for loose breaker
I was also going to say check for loose connections. Do you have aluminum wiring? Have you had large loads plugged into outlets lately, like say an A/C? Has it been really hot there lately? - But if you measuring 98V right at the terminal of the breaker (and not just at a receptacle) then maybe this is not your problem.
If your measuring 98V at breaker terminal, turn off breaker, remove branch circuit wire from breaker, turn breaker back on and remeasure voltage at breaker terminal. If it's still 98V and all other breaker's are at 120V, then the breaker (or it's connection to the panel) is the problem and not the circuit wiring.
Edit: ^ Sort of the same thing EddieWalker said as I was typing this (but in reverse order).