I Beam flex???

/ I Beam flex??? #1  

DrDan

Gold Member
Joined
Apr 16, 2001
Messages
351
Location
Ohio
Tractor
G1800 & BX2200
I am putting in an overhead crane in my shop and have a question. The shop is 30' wide X 40' long. We have no problem supporting 4" I Beam by hooking on to 2" X 6" trusses spaced 7.5' OC. Lots of support especially since these beams will be alongside the walls. Now here's the problem. We will be running a bridge across the 30' width and hooking it onto the I beams running alonside the walls on each side. This bridge will roll on the two I beams with steel rollers rated at 1.5 ton. On the bridge will be another trolley (steel rollers) that will go back and forth with the lift mounted to it. The I beam used for the bridge can't flex much more than 3/8" when the lift is picking up a ton or the trolly will roll to the center. The idea is to be able to get this lift anywhere in the shop. I am also being told that we won't need any power drive on the bridge since the steel wheels roll so easy on the steel I beam. Anyone know how much 4" or 6" I beam 30' long will flex when supported by the ends and a ton is hung on the center?

DrDan
 
/ I Beam flex??? #2  
The formula for a deflection of a beam supported on the ends with a centered load is: (Force * length^3) / (48 * E * I)
E = modulus of elasticity
I = moment of inertia.

For structural steel, E = 29 Mpsi
I is calculated from the dimensions of the beam

I looked in a book for standard I beam data. There are 2 sizes listed for both the 4" and 6" I beam.
a) 4" beam with .193 thick web - I=6.08 in^4
b) 4" beam with .326 thick web - I=6.79 in^4
c) 6" beam with .232 thick web - I=22.1 in^4
d) 6" beam with .465 thick web - I=26.3 in^4

Putting the numbers into the formula:
(2000 * 360^3)/(48 * 29E6 * I)
This reduces to:
67/I
Therefore using the I values from above:
a) 11.02 in
b) 9.87 in
c) 3.0 in
d) 2.54 in

Clearly neither the 4" or 6" beam will meet your 3/8" max deflection requirement.

Using the reduced formula above, and 3/8", and solving for an I value: 67/I = .375, we get I=178.7

I went back to the beam tables and looked for the minimum sized beam that had an I value greater than 172. The minimum sized beam that will meet your requirements is a 12" beam. The book I have lists four different web sizes for a 12" beam (.350, .428, .462, .687). Any of these will work.
The dimensions for the .350 web beam are:
Flange width = 5.0 in
flange thickness = .491 in
I = 218
Its designation is S12 x 31.8.
This beam weights 31.8 #/ft, therefore 30 ft = 954 # beam.

If you really want to use the best 6" beam from above, we can put all the numbers into the equation and solve for max weight at 3/8" deflection. The answer: 294# is the max weight you could suspend at the center and have 3/8" deflection. -- Not a very useful crane.

You may need to look at the supporting 4" beams as well, to make sure they can take all the loads.
 
/ I Beam flex??? #3  
Nice work rlw, I was finding the same but didn't find pre-calculated moment numbers for the beams, only a formula which was giving me fits. There is probably a calculator somewhere on the 'net to do all this with dropdowns or something.

Whatever the case DrDan, you do want to be extra careful when designing for overhead lifting. Check with your local crane and hoist dealer and maybe they can give you some help /w3tcompact/icons/smile.gif
 
/ I Beam flex??? #4  
<font color=blue>Check with your local crane and hoist dealer and maybe they can give you some help</font color=blue>

Just don't check with <A target="_blank" HREF=http://www.tractorbynet.com/forumfiles/35-210572-whoops02.jpg>these</A> guys (from another post on TBN). /w3tcompact/icons/laugh.gif
 
/ I Beam flex??? #5  
Ouch! I'm a big crane fan and have come across various crane failure pictures over the years. They are typically pretty spectacular. Several years ago we had a large lattice boom crawler crane fall into the river while working on a bridge project. Fortunately, the operator was not hurt but the extraction was even more impressive than the planned lift /w3tcompact/icons/smile.gif
 
/ I Beam flex??? #6  
rlw - On a similar note, I have been trying to figure the best way to build a bridge across a creek to get my tractor across. I need a span of about 24' and the tractor weighs about 3500#. From your numbers, looks like two 12" I beams would safely support that weight. I would space the I beams where they would be approximately under the wheels on each side. And also have the appropriate cross bracing between the I beams to prevent rolling.
 
/ I Beam flex??? #7  
bbx - try and find an old flatbed trailer. If you can get it to the area all you need to do is cut the rear axels off and you have a ready made bridge 8 feet wide x 35-40 feet long and strnog enough to drive over. I've read in Farm Show Magazine of people getting trailers for $150 and even welding two together to makde a wider bridge.
 
/ I Beam flex???
  • Thread Starter
#8  
Thank you rlw... That gives me some "food for thought". In actuality I will only be lifting less than 1000# (more often 300-500#), so now I can get some better ideas of my limitations. Actually the 6" looks like it would do it!

You see, I am in a wheelchair and do a lot of bowl turning on the lathe and handle lots of stumps that must be split and then moved to the lathe and chucked up. LOL You should see the underpinnings on my lathe! Of course I can settle for 6 to 8" bowls. I don't get my "jolly's" uless it's 20" or greater!

I'll be back to you later. Gotta go to work!

DrDan
 
/ I Beam flex??? #9  
DrDan,

How about a couple photos of your larger bowls...maybe in the photos forum?

Love to see them and a pic of the lathe you turn them on too!

Bill in Pgh, PA
 
/ I Beam flex??? #10  
DrDan,

To bad you are in Ohio. I got plenty of stumps for you. Just
come and get 'em. /w3tcompact/icons/smile.gif

I to would like to see what you have made. I've got some
large 36+ inch oak stump that would make a heck of a bowl.
/w3tcompact/icons/smile.gif

I'm real impressed that people figured out the span data for
you. The other to consider is how you are going to support
the beam. You mention the trusses but could the handle
the load. The other option is to build the structures under
the beam ends.

I know enough to be dangerous and I bought some wood
engineering texts and standards manuals a few months ago
to study some building ideas I came up with. From a dollar
perspective I would have been better off just paying an
Engineer but I wanted the books, span tables, and knowledge.

But you might want to talk to a Engineer. A friend at work
had a concern with a house he was buying and the Engineer
was a few hundred dollars to look at the problem and design
a solution. The Engineer's stamped solution was MUCH
cheaper than what various contractors bids. A couple
hundred dollars for the Engineers solutions to multiple
thousand dollars for the contractors......

Let me know when you want the stumps!
Dan McCarty
 
/ I Beam flex??? #12  
Dan,

First I think you'd want it rated for at least 1 ton. Seems like a lot of time & money to invest to move 300#. Probably better off with some kind of motorized portable crane for the smaller load.

Need more info on these 2X6" trusses. Wood or metal? Typically overhead cranes are supported on vertical steel I beams that are also cross braced. May be worth contacting a crane installer & have the sales rep out for a visit. He can show you some installations & you can pick his brain & maybe buy a component or two from him.

There is value in buying the crane as an installed package, one entity is responsible for the safety & performance of the system. Even being an egineer myself, I lean towards a single source integrated solution just for the liability.

Another option is to have a professional mechanical or civil engineer design & specify the system & then you can build it yourself (probably need some hlep as that steel is HEAVY!)

Good luck. Sounds like a fun project.
 
/ I Beam flex??? #13  
RobS - I was lucky to actually have a table that included moments of inertia - I don't usually get lucky.
Here is a quick and dirty formula for I-beams in case others want to play with the numbers. It's slightly off since it doesn't account for radii, etc. I checked it against the listed values - pretty close, just a little less - which will help provide a little safety factor.

Definitions:
FW = flange width
FT = flange thickness
H = height of I beam
WT = web thickness

I = (FW * H^3) / 12 - [(FW - WT) * {H-(2*FT)}^3] / 12

Note that this is NOT VALID for an I beam laid on its side.
 
/ I Beam flex??? #14  
My concern with your design would be the support of this entire system on 2 x 6 trusses on 7.5' centers. I can't picture a truss supporting that load even close to the ends, as you mention. Also, how much flex will the 4" I-beam have between the 7.5' centers where it is supported by the truss? If I understand the description, the 4" I-beam will be supporting one end of the 30' bridge as well as the rolling trolley with its weight plus anything it is lifting. Am I missing something?
 
/ I Beam flex???
  • Thread Starter
#15  
I will post some pix's of bowls later. Right now I have either sold them or have them on consignment. I will be starting to turn American Chestnut bowls very soon. Yes the American Chestnut that is rare and endangered. I had an ailing one in my side yard and it had to come down to clear my building... Made me sick cutting it down, so the least I can do is show my reverence and make beautiful bowls out of it.

DrDan
 
/ I Beam flex???
  • Thread Starter
#16  
Ok, the trusses are actually 2" X 8" and fit into a mortise on the top of (3) 2" X 6" that are laminated together using screws and glue. Super stout building. Each truss sits on a column which are imbedded in a 24" diameter X 4' deep concrete pad.

I see no use for the lift going right to the walls so I will mount the longitudinal beams in about 24" from the columns. Originally I had thought about 4" X 4" steel columns to support the longitudinal beams, but they will "always" be in the way! In addition I have the heat in the floor and have to be careful with drilling into the floor to mount anything. The best plan is to hang them off the trusses if I can do so safely.

So we are actually talking a bridge of 24' and I guess I can tolerate a little more flex than 3/8" An inch or 1.5" would not put too much of a valley in the center and cause the trolley to roll towards the middle.

I am definitely on a budget here and can't even consider having a crane company come in and do the job. Originally I considered making the bridge motorized and bought a gear motor on eBay, but with good trolleys (I am thinking about the Jet 1.5 Ton for each end of bridge) with ball bearing steel wheels I think I can get away w/o powering the beast.

How much flex would there be on the heavy web 6" I-Beam at 24' long with 1000# on it?

Yes I love cranes also. I buy alot of steel (I also do ornamental iron work) and just love to watch the crane at the steel suppliers. It's a 26 Ton with double powered lifts on the bridge. Bridge must be 100' long. I watch them lift an 18 ton beam off a truck the other day (from a distance) and it handled it like a baby!

Love it! Used to work at Fairbanks Morse when they were still building railroad switch engines. Saw two manned overhead cranes pick up the whole engine several times. Like I say, I think cranes are one of my loves!

Actually I would love to put two lifts on the bridge. It is so cool the things you can do when you can lift both ends of long objects.

So I'm having a ball thinking over the options and appreciate all your help guys. Yes money is an object so I have to come up with a workable plan. Can't really put much more than $4000 to $5000 into the total package. That cuts out the commercial boys!

DrDan
 
/ I Beam flex??? #18  
Hi Dr Dan

Some years back i made a beam to spand 20' that i lifted bulka bags of fertilizer about 1ton. this beam i made out of 2" reject exhaust pipe laminated 6 pieces together and 2 top and bottom like this (end veiw) never even flexed a mm
.OOO
.. O
.. O
.. O
.. O
.OOO
 
/ I Beam flex??? #19  
DrDan, I hate to throw cold water on a hot fire, but unless I'm reading things wrong, you are headed for some trouble with a bridge crane. First, alignment of the rails and bridge is critical, or the bridge will crab and lock up. The jet trollys would give you trouble, unless you double up on them and but a 4 foot beam between them.
The big question in my mind is do you need as much crane as you are engineering? Wouldn't you be able to use a double A frame with a beam across the top and a good set of casters on it to accomplish your goal? I've built a couple of that style and find them far more useful than a bridge since they can be moved in and out of place relatively quick. We have no trouble moving them with 1800# hanging on the 8" casters on a concrete floor.
 
/ I Beam flex???
  • Thread Starter
#20  
My shop is too crowded with machines for that Franz

DrDan
 

Marketplace Items

KUHN KNIGHT SLINGER 8118 SPREADER (A63276)
KUHN KNIGHT...
Kubota V3300-T Turbo Diesel Industrial Engine  84 HP  Pump Takeout (A63689)
Kubota V3300-T...
2013 FORD E-350 11 PASSENGER VAN (A65643)
2013 FORD E-350 11...
3ft Metal Chevrolet Tailgate (A65583)
3ft Metal...
Jack Daniels Metal Sign (A65583)
Jack Daniels Metal...
Used Landpride GR1525 Stump Grinder
Used Landpride...
 
Top