This is from my understanding of hydronic radiant heat. I see flow rates in the 5-6-7 gpm range for floors being typical. I have never been able to get mine above 3 gpm, and frankly 1.6-2 is much more common. This is pretty low for hydronic tubing as I understand it. And apparently increased flow leads to more heat transfer. I doubt we are approaching turbulent flow in any of these cases, as that would seem anathema to the circulating pump mode, but it is a key item that has vexed me.Why do you think that increasing the flow will make much difference to the heat in the house?
Have you done some tests? There isn't much of a temperature differential between the concrete next to a heat tube and the fluid inside, so I wouldn't expect the heat to move into or thru the concrete very quickly.
My thinking is that if you are able to ncrease the flow rate through the piping, you will see the return flow will be warmer than before - and the concrete surface temperature will not change much.
rScotty
QSF: You reminded me of another point from my history with this. My shop runs at 120F (and perfectly fine at that). The house started at 120F but due to the low flow I had issues getting enough heat so I eventually bumped it to 130. Everyone tells you to use numbers like 90F for a floor, so I was thinking I was already out of bounds at 120 and so 130 was nutzo, but it did improve output and worked a lot better. It did not occur to me that perhaps I could just bump it to 140 when it is really cold, so I will give that a shot this winter, when the time comes. So thanks for that memory jog and suggestion.
And while I get what you are trying to show with your example of air temps and output, I find things are never that 1:1 easy when it comes to concepts like heat transfer, but the direction you are pointing makes sense.