It depends on how fast you want to blow it -- 10sec~ 50mV, 4sec~150mV not counting the losses inherent in each conection to the fuse [another couple mV per under load for GOOD connections]. Multiple fuses just add these losses and altho they are small, the inverter will have a fast acting low voltage cutoff somewhere above 10V. Loss of an extra tenth of a volt or three can be real significant when losses under high load in the battery, wiring and fusing add up to limit the inverter supply to near its cutoff. Thats when the fusing turns into a nuisance.
larry