bones1 said:
...Tom, can you elaborate on this.I do have trusses above where the beam would go but do you mean support it on the ends and attach to the trusses?.
That comment came from a background in which minimum weight had prime importance with cost being secondary. In this case, a single simply supported beam is probably your minimum cost solution.
What I was thinking was, if your hoist trolley rides the top surface of the beam, the top plus at least one side of the beam would have to be kept free of obstructions to allow the hoist to traverse. In that case, a simply supported beam would be about the only choice. But, if the trolley rides a track attached to the bottom of the beam (which has it's own design challenges) there is a possibility that the beam could be tied to and supported by existing or additional building structure.
The trusses I see in the pictures look to be standard roof trusses - 2x4 lower chords and braces with 2x6 upper chords. They are normally designed for expected roof loads plus 200# vertical load on the lower chord (primarily to accommodate personnel walking the beams during construction). I wouldn't consider them as candidates for significant support for your hoist. Especially since it appears your installation will run parallel to those trusses.
You could, again assuming that the hoist trolley rides the bottom of the beam, install a truss in which your beam is the bottom chord. That could minimize the size and weight, but would likely be a more expensive solution.
Since the beam must be designed for stiffness rather than strength, and steel is some 20x stiffer than wood (Young's Modulus for steel is about 30x10^6 and about 1.5x10^6 for wood), I suspect that your best, most satisfactory solution would be a simply supported structural steel I or H beam with the hoist trolley riding the lower flange of that beam. That would essentially remove the concern for beam instability mentioned in an earlier post and should be a simple, straightforward installation.
Using the assumptions previously stated, a simply supported standard I-beam 10" deep by 4.66" wide (25.4 #/ft ~ 750#) would be sufficient to meet the bending loads with the stated safety factor. This, in no way constitutes an engineering analysis and is no guarantee the beam is suitable for the purpose.