I regularly run my Lincoln WeldPak 100 on a 12/3 extension cord without difficulty. (Don't get too worried about the differences between the 100 and 125, they both draw the same current and have the same welding output, it's a marketing ploy to label the newer one a "125" but I digress).
There's two main things to consider when sizing wire: the ampacity, and the voltage drop. A 20 amp circuit according to the NEC requires 12 ga wire, with a few exceptions being allowed (one is welding where the duty cycle can be factored in). 14 gauge likely would be allowable for a 20 amp dedicated welder circuit (I suspect, without doing the math).
The other factor though is voltage drop. Wire is a resistor, according to Ohm's Law it will drop voltage as a function of the current going through it times the resistance (V=IR). For high current loads, and long runs, voltage drop becomes significant. Pull 20 amps through a 100 foot 12 gauge extension cord? The voltage on the outlet end will be quite lower than the -120 volts or thereabouts- on the supply end. The solution is to shorten the extension cord, or get a heavier gauge cord (like a 10 gauge).
To your problem, though, which is how to weld without tripping breakers. I try to find an outlet which only has one thing on it, preferably an appliance outlet--like the dishwasher (I use my dishwasher outlet a lot and run the extension cord out the kitchen window). Or the washing machine outlet. (Of course don't run either of those appliances while you weld if you're plugged into their circuit). You should look in your breaker box to see if there are ANY 20 amp circuit breakers, if so use the receptacle on that circuit and unplug any other loads from that circuit. Even if the other loads are only lights.
Use the shortest, heaviest extension cord you can to get from the receptacle to your work.
Proper welding technique helps too. Keep the correct stickout, around 3/8 or 1/2 inch, not shorter. If you're constantly getting the tip shorted to the work it'll draw more current and trip the breaker.
I don't recommend sticking a 20 amp breaker where there is presently a 15 amp.
There's two main things to consider when sizing wire: the ampacity, and the voltage drop. A 20 amp circuit according to the NEC requires 12 ga wire, with a few exceptions being allowed (one is welding where the duty cycle can be factored in). 14 gauge likely would be allowable for a 20 amp dedicated welder circuit (I suspect, without doing the math).
The other factor though is voltage drop. Wire is a resistor, according to Ohm's Law it will drop voltage as a function of the current going through it times the resistance (V=IR). For high current loads, and long runs, voltage drop becomes significant. Pull 20 amps through a 100 foot 12 gauge extension cord? The voltage on the outlet end will be quite lower than the -120 volts or thereabouts- on the supply end. The solution is to shorten the extension cord, or get a heavier gauge cord (like a 10 gauge).
To your problem, though, which is how to weld without tripping breakers. I try to find an outlet which only has one thing on it, preferably an appliance outlet--like the dishwasher (I use my dishwasher outlet a lot and run the extension cord out the kitchen window). Or the washing machine outlet. (Of course don't run either of those appliances while you weld if you're plugged into their circuit). You should look in your breaker box to see if there are ANY 20 amp circuit breakers, if so use the receptacle on that circuit and unplug any other loads from that circuit. Even if the other loads are only lights.
Use the shortest, heaviest extension cord you can to get from the receptacle to your work.
Proper welding technique helps too. Keep the correct stickout, around 3/8 or 1/2 inch, not shorter. If you're constantly getting the tip shorted to the work it'll draw more current and trip the breaker.
I don't recommend sticking a 20 amp breaker where there is presently a 15 amp.