Welders are unlike other devices that you wire based on breaker/wire sizes. When you go to the code book, it shows you how to figure wire size based on the welders DUTY CYCLE. A 100% duty cycle welder will require the wire be protected by a breaker no larger then the maximum current carrying ability as established in the NEC wire chart. From there however, you can derate it, that is, provide a larger breaker then the wire would normally be sized for. The logic is the wire will easily handle the larger current for a short duration. That circuit will be dedicated though for a welder. You see this also in home uses for AC units where a 40 amp breaker may feed a #10 wire when used in a dedicated AC circuit. The reason is because of the high compressor start up demand and relatively low operating current demand. On the AC unit you will see minimum circuit size and maximum fuse size, this is your guide to sizing the wire adequately. My AC unit has a brief start up current of 102 amps yet runs at 17 amps. A #10 wire is all that feeds it. This is per code in my area.
PS - As I remember, a 20% duty cycle allows you to weld 2 minutes out of every 10 minutes. If you continually exceed this duty cycle, it will overheat the transformer, ask me how I know this. /forums/images/graemlins/grin.gif