New electrical panel question

/ New electrical panel question #41  
I suspect it is not unusual to pay more for 3 phase service. They are probably using 3 transformer set up, which costs them more.

I wonder how many people really know how many amps they draw.

Easy enough to figure it out from your power bills but PGE doesn't make that easy with all their baseline tiered mumbo jumbo to get more money out of your pocket. IMHO power should be billed at a flat rate for everyone based on costs, enough of this socialism and gubberment mandated kinda stuff.
 
/ New electrical panel question #42  
I'm trying to think how that would operate two fridges, a freezer, electric stove, microwave, toaster, coffee pot, hair dryer, electric water heater, electric well pump,electric clothes dryer, 22Kw of electric heat, block heater on the tractor and water heat trace for the critter's water pipes.
Then if we ever dialed the welder up to 300amps.........

30a does sound small for a 3bdrm house. But being 30a 120v I am guessing dryer, water heater, stove are gas as well as heating???

Take all of the 240v stuff out of a house, and it dont need much amperage.
 
/ New electrical panel question #43  
Easy enough to figure it out from your power bills but PGE doesn't make that easy with all their baseline tiered mumbo jumbo to get more money out of your pocket. IMHO power should be billed at a flat rate for everyone based on costs, enough of this socialism and gubberment mandated kinda stuff.
That "fixed" vs. "usage" charges have been mandated for years in Wisconsin. Everybody shares in the costs of maintaining the infrastructure (the "fixed") that way...whether you use 1 kwh or zillions per month you still need the ability to get it. From there you pay on what you use. Now I realize there is a lot of "cost accounting" involved (that $2,000 hammer) but here they are watched closely by people that are hardly fans of the utilities.
 
/ New electrical panel question #44  
I'm trying to think how that would operate two fridges, a freezer, electric stove, microwave, toaster, coffee pot, hair dryer, electric water heater, electric well pump,electric clothes dryer, 22Kw of electric heat, block heater on the tractor and water heat trace for the critter's water pipes.
Then if we ever dialed the welder up to 300amps.........
Grew up in a house with 60a service which I guess was "premier" for its time (mid 50's build). Number of devices has certainly increased but the draw has decreased (evidenced best by the utilities trying to shift costs to the "fixed" side from the "usage" side). But I agree...100a minimum today, 200a better.
 
/ New electrical panel question #45  
All these homes were built in 1922 and I bought from the original owner... have had a family of 5 living there with 3 teenage daughters.

City water, gas heat, gas cooking, gas water heater and gas clothes dryer... never freezes or gets hot... Oakland really has an ideal climate... the home does have a gravity central furnace with large ducts... no fan or blower...

The week power was out after the 1989 SF Earthquake I did OK... still could cook, had hot water, heat and cooking.

My neighbors with the upgraded 150-200 amp panels and modern furnaces and self cleaning ranges didn't do so well...

Always did laundry on Saturday and used a counter-top Microwave... so not totally primitive.

I've owned the home 31 years and the 5 years I lived there I never replaced a fuse...

The family with 3 girls had problems when they first moved in... seemed they all had hairdryers and curling irons and wanted to use them at the same time...

I want to relate the most extreme example I have come across... it is a 3 unit triplex built as a duplex in 1928 with a legal basement unit added during WWII.. so three legal units...

The entire Triplex is on one single 30 amp Edison Fuse Main... so the Landlord pays for Electricity... each unit has an individual gas meter...

Really shows were we were and where we are...
 
/ New electrical panel question #46  
Grew up in a house with 60a service which I guess was "premier" for its time (mid 50's build). Number of devices has certainly increased but the draw has decreased (evidenced best by the utilities trying to shift costs to the "fixed" side from the "usage" side). But I agree...100a minimum today, 200a better.

My brothers 2200 square foot home after his three additions still has the original 220v 60amp cartridge fuse main...

Also extensive use of gas... he does have central HVAC with a 30 amp circuit.

Sold the home two years ago in a bidding war for 840k with the 60 amp service...

Home Inspector came out and noted the size, looked under the cover and noted is was original 1950 with permit.

The house had many inspections and each inspector said it was one of the best maintained homes they have come across... you see I did all the work!
 
/ New electrical panel question #47  
Easy enough to figure it out from your power bills but PGE doesn't make that easy with all their baseline tiered mumbo jumbo to get more money out of your pocket. IMHO power should be billed at a flat rate for everyone based on costs, enough of this socialism and gubberment mandated kinda stuff.

Trying to figure out how much power (amps) one draws from your energy usage (bill) is like trying to figure out what your (maximum) speed was by using your odometer and a stop watch.
You can only figure out your average speed, not your peak. (e.g. like saying if I went 100 miles in 2 hours, I must of only been driving 50mph. See if a cop buys the argument. Paying attention to peak, not average, is the important part if your sizing breakers and conductors or avoiding speeding tickets.
 
/ New electrical panel question #49  
I've been using these around the Hospital Campus to track usage, peak usage and other useful Data...

Home | E-Mon
 
/ New electrical panel question #50  
Trying to figure out how much power (amps) one draws from your energy usage (bill) is like trying to figure out what your (maximum) speed was by using your odometer and a stop watch.
You can only figure out your average speed, not your peak. (e.g. like saying if I went 100 miles in 2 hours, I must of only been driving 50mph. See if a cop buys the argument. Paying attention to peak, not average, is the important part if your sizing breakers and conductors or avoiding speeding tickets.

The best way to measure peak current draw is to use clamp-on amp meters, which I have a couple of anyway.
Of course you size the conductors for the max anticipated current draw of the circuit then size the breaker to the conductor. The purpose of the breaker is just to keep your house from burning down. Trouble is you have to anticipate up front what you'll need down the road or you'll end up likely paying more if you didn't plan for enough.
 
/ New electrical panel question #51  
Trying to figure out how much power (amps) one draws from your energy usage (bill) is like trying to figure out what your (maximum) speed was by using your odometer and a stop watch..

Power is Watts, Current is Amps.

but you are right, your load changes all the time. Your bill is your best guide for what you are using.

I wouldn't put in less than a 200A panel for a house, with lots of breaker space. I like to put in a lot more circuits than the minimum.
 
/ New electrical panel question #52  
Power is Watts, Current is Amps.

but you are right, your load changes all the time. Your bill is your best guide for what you are using.

I wouldn't put in less than a 200A panel for a house, with lots of breaker space. I like to put in a lot more circuits than the minimum.

Nether would I. Heck if I could, I'd get more. Get as much as you can, while you can.

BTW I'm a retired EE, just so you know, but I wasn't going to get all into power factors and what not. LOL
 
/ New electrical panel question #53  
Seems to me the OP asked for opinions on 100a vs 200a service

So, completely renovating and adding on to a 1940s farm house. My question is, what size of service should I go for? 100amp or 200 amp?...

So, some of us getting by with 30a, 60a, or the like or needing 3 phase really has nothing to do with his question.

I know in our area, if you do any kind of initial build or replace a service the minimum you can now legally install is 100a - so discussing less than 100a would not even apply - this could be true of where he lives.

Now, as to the original question, if you are going to replace the drop and the panel, I'd go with 200a - makes adding any additional sub panels much easier. I would probably want a "pass-through" panel.

Some utility companies will give/install the meter base free of charge - I would ask! I did and they gave me what I needed even though I could but it at a DIY. They often do this because they know the meter base they hand out is an exact fit and gauged to fit their meters and power requirements.

Our power company also does not charge to upgrade the transformer or the drop from their transformer to the weather head. If underground, you have to provide the conduit, properly sized and buried to depth and they will provide the drop.

Make sure you know what you have to pay for and what they will provide before you decide what to do and work within you budget. Often they will let you pay for everything instead of volunteering that they will provide some of the materials unless you ask.
 
/ New electrical panel question #54  
For those not intimate with the subject, a clamp-on will tell you amps. If you multiply amps times volts, you usually do NOT get watts. What you will calculate is VA, or volt-amps. To find watts you must also know the power factor of the device or circuit. Watts=VA times PowerFactor. There are meters that will measure watts, often called a true wattmeter (FYI home electric meters, old disk types and newer solid state models, DO measure true watts). Home devices like Kill-A-Watt and the Energy Detective do measure true watts. Many people are fooled when they use a clamp-on and measure a lightly loaded electric motor and see that they think it is using 20-30% power with little load. In reality if power factor is taken in consideration the motor's load is low and close to what you would expect.

Home "energy saving" devices can help improve power factor a bit, but since residential consumers do not pay for VA or bad power factor (larger industrial users do pay for bad power factor), there is only a few penny's a year of savings.

paul
 
/ New electrical panel question #55  
OK. Please educate me on this. If I have a 100 Amp wire to the service entrance, and put in a 200 Amp panel, but change out the main breaker to be a 100 Amp breaker, what is wrong with that?

I know I have to upgrade the main feed wire to put the 200 Amp breaker back in, but if I ever need the 200 Amps, I don't have to change out the panel. And, I get a lot more breaker slots. As people have said, with LED lights and more efficient appliances, real amperage draws are decreasing, but the number of circuits desired seems to be increasing.

Nothing wrong with what you descibe as long as the main matches the wire to the service entrance.
 
/ New electrical panel question #56  
If you're changing the service to underground anyway it's a no brainer to go with the 200A service if not more if you can get it. Heck, I wish they'd run 3 phase so I could run 3 phase motors easy.

Agree, given that info.. go with 200 amp and don't give it a second thought.
 
/ New electrical panel question #57  
I think some people are getting past the subject.

Talk to an electrician ask for a quote on 100 amp service and 200, see what it comes in as. Think about what your need are. Will you be running a 3 phase ________? Do you think you will be putting in a bunch of big motors, and have your buddies over running them the same time?

Talk to your utility about meter charges, and see what makes a difference.

Sure somethings help when selling a house. But doesn't mean it hurts if you don't have them. Lots of things go into the buying deciscion of a home. I doubt they will go screaming away if you have 100 service, then may not even know what a 200 is.
 
/ New electrical panel question #58  
How many people need 3phase motors, or have desire to have one?

The chance that you will need 3 phase service is about 1%, if that.
 
/ New electrical panel question #59  
How many people need 3phase motors, or have desire to have one?

The chance that you will need 3 phase service is about 1%, if that.
On used woodworking equipment there are some great deals on well-maintained 3ph equipment (mostly from school shops). I guess the phase converters have gotten cheaper and more reliable to let them run on 240v single phase so the costs of installing 3ph doesn't make sense to me.
 
/ New electrical panel question #60  
On used woodworking equipment there are some great deals on well-maintained 3ph equipment (mostly from school shops). I guess the phase converters have gotten cheaper and more reliable to let them run on 240v single phase so the costs of installing 3ph doesn't make sense to me.

Yes I have heard you can get 3 phase machinary cheap at times, since it can be hard to sell.

But has anyone asked him if he plans on having some big *** machines, or if he even have room on the property to put a shop? What does 3 phase service cost?
 
 