buckeyefarmer
Epic Contributor
I prefer QO over homeline, just a personnal preference. Watch out for counterfeit QO breakers.
Power is Watts, Current is Amps.
but you are right, your load changes all the time. Your bill is your best guide for what you are using.
I wouldn't put in less than a 200A panel for a house, with lots of breaker space. I like to put in a lot more circuits than the minimum.
Yes we know, I won't bore people with how power is directly related to amps (and power factor), that wasn't my point. My point was that you can't correlate power needs to your energy usage bill.
Imagine 2 monthly power bills (240V service):
One is for 4147 kw-hrs, the other is for 864 kw-hrs.
Which one can get by with 30 amp service, which one needs a 200A service?
There"s no way you can tell.
(e.g. A 30 amp service pulling 24amps (24hr for 30 days) is the 4147 kw-hr bill, a 150amp load that only runs for 1 day a month is the 864kw-hr bill and needs a 200 amp service.)
Sizing a service is where we try to apply science, engineering, formulations, calculations, etc..; but in the end it's more similar to a soothsayer trying to look into a crystal ball and predict the future.
Sort of like buying insurance.
Easy enough to figure it out from your power bills but PGE doesn't make that easy with all their baseline tiered mumbo jumbo to get more money out of your pocket. IMHO power should be billed at a flat rate for everyone based on costs, enough of this socialism and gubberment mandated kinda stuff.
When I first started working at the Hospital... the environmental controls were all set to start in each building at exactly the same time... this caused a momentary spike in usage as the compressors and blowers were all starting together.
By staggering the start times by 15 minutes I was able to reduce cost based on maximum peek for the billing cycle.