...We have an opportunity to buy some 4'x8' sheets of 2 1/2" thick polyiso foam board that is faced with a fiberglass layer on both sides, at a very good price. Our plan is to install this on the roof purlins, which are 2x4's on end, that run parallel to the ridge.
One of our members, a former roofer, has concerns that condensation may form in the cavities (24" x 3 1/2") formed by the covering of the purlins. The building is heated as best we can, about 5 hours a week, in the winter.
Should we be concerned about this, and if so, is there a cheap way to mitigate it?
If I understand your question, you are going to install the panels to the bottoms of the purlins, not between them? And since you are installing them to the bottoms of the purlins, you will create a 3 1/2 inch air gap between the panels and the metal roof. This gap will allow condensation to form on the bottom of the metal, and that condensation will have no way to dry out or drain away.
The smaller the air gap that you have, the less condensation you will have. Without removing the metal roof, and doing this as cheaply as possible, I would strongly suggest cutting and fitting the panels in between each purlin. There will still be a small amount of condensation that forms, but I doubt it will be enough to worry about. The best way to deal with that small amount of moisture would be a ridge vent. Home Depot sells a metal ridge vent for a fair price that could easily be installed over your existing ridge. Just drill holes near the peak of every roof panel so air can flow out of there. Cooler air will enter under the roof at the eaves, and rise up along the underside of the metal, drying out the metal, and exiting at the ridge peak.
Here is a picture of the Home Depot ridge vent that I put on my chicken coop.
View attachment 598298
Thanks, Eddie. You've pretty well got the picture except that it's a wooden roof with shingles, and a ridge cap. The purlins are about 2" apart at the ridge, one centered, and one on each side of it.
... and that is a potential breeding space for dew point issues, not just with heat on the inside, also when the building is unheated and a spring or fall sun angle is sufficient to heat that roof and plywood notably with a cold shell below.
I don't understand how this can cause condensation on the inside of the roof.
This tablet just nuked a better response so here is the condensed version. We know warm air suspended more moisture than cold. My old thermopane windows will ice up surprisingly and wet the sills if I drop a tight fitting fabric blind with just 35% RH and a 5-10 degree night. Blinds have to go up in those conditions. Reason that forms ice (water first of course) is because I trap the air there in narrow confines with no air movement. The water is still forming, more of it actually as the air temp in front is the glass is higher with the blind up, but the 35% air moving across the glass allows it to evaporate. So when hot and cold membranes (underside of cold plywood and relatively warm upper insulation surface) are in close proximity and you trap that air, that is a space begging to condensate. No transport air exists to evacuate it.
The reason people get away with spray foam directly applied to roof sheathing is the air is fully removed, so the moisture transport mechanism (air) can't deposit it. Just because someone tightly fits rigid insulation between purlins or trusses does not mean air doesn't get there (in the narrow voids) and change out over time. So moisture is carried in waiting for a temp differential without enough air movement to evaporate it. The reason I don't recommend spray foam directly applied to roof sheathing either, is any minor breach in the roof membrane (and even well installed roofs have this at some place or point in time) traps that moisture in the substrate. Quite the rotted mess mess if you've ever torn one apart.
You are trying to equate glass with plywood/OSB sheathing. They are not remotely similar. Glass conducts heat around 9 times better than wood. Yes, condensation is based on warm air and a cool/cold surface, but the rest of your explanations are not at all relevant.
This tablet just nuked a better response so here is the condensed version. We know warm air suspended more moisture than cold. My old thermopane windows will ice up surprisingly and wet the sills if I drop a tight fitting fabric blind with just 35% RH and a 5-10 degree night. Blinds have to go up in those conditions. Reason that forms ice (water first of course) is because I trap the air there in narrow confines with no air movement. The water is still forming, more of it actually as the air temp in front is the glass is higher with the blind up, but the 35% air moving across the glass allows it to evaporate. So when hot and cold membranes (underside of cold plywood and relatively warm upper insulation surface) are in close proximity and you trap that air, that is a space begging to condensate. No transport air exists to evacuate it.
The reason people get away with spray foam directly applied to roof sheathing is the air is fully removed, so the moisture transport mechanism (air) can't deposit it. Just because someone tightly fits rigid insulation between purlins or trusses does not mean air doesn't get there (in the narrow voids) and change out over time. So moisture is carried in waiting for a temp differential without enough air movement to evaporate it. The reason I don't recommend spray foam directly applied to roof sheathing either, is any minor breach in the roof membrane (and even well installed roofs have this at some place or point in time) traps that moisture in the substrate. Quite the rotted mess mess if you've ever torn one apart.