The answer is not really simple. Well, it could be but there are a lot of things to look at here. You did not mention if the cable has Aluminum or Copper conductors. Could make a difference here. You didn't say how many "several years ago" was. The conductors could be 60ー, 75ー or 90ー rated. Are they type UF, THWN, THHN, THWN-2, XHHW, XHHW-2? It makes a difference.

Let's say it's copper type THWN-2 and they were 90ー rated, such as in type NM-B cable.
First, NEC Article 110-14 says if the circuit is under 100A then the conductors need to be used at their 60ー rating, unless all terminations in the circuit carry a higher rating. #6 copper at 60ー is able to be used at no more than 55A. However, there is a way out here. According to NEC 240.6, 55A is not a standard fuse/breaker size so you are allowed to round up the the next standard size which is 60A. So if you had a 6-3 type NM-B cable run, you are good to go with a 60A breaker on a 45A load.

Now, let's say it is Aluminum conductors.
#6 at 60ー is only good for 40A according to NEC 310.16 and 110.14

So I need more info to accurately answer your question. Post what cable type was run and I'll try to help more.

Great Post to help a friend!!!
 
   / Simple Electrical Question (hopefully)
  • Thread Starter
#12  
Thanks a bunch, I'll be glad to use the tub to it's max features.
 

Tractor & Equipment Auctions

2014 International DuraStar 4300 Terex BT3063 30,000LB Crane Truck (A48081)
2014 International...
New/Unused Fuel Pump with 50ft of Hose (A51573)
New/Unused Fuel...
2018 Freightliner Day Cab, Detroit Diesel, Auto (A52384)
2018 Freightliner...
2017 INTERNATIONAL PRO STAR (A52472)
2017 INTERNATIONAL...
BUSH HOG 3308R-2 LOT NUMBER 118 (A53084)
BUSH HOG 3308R-2...
New Skid Steer Attachment Plate (A53002)
New Skid Steer...
 
Top