Small diesel generators

/ Small diesel generators
  • Thread Starter
#21  
I have an Onan commercial quiet diesel genset 5500 w that I have had for 5 years. Very quiet and burns about .6 gph at full load. This has a Kubota engine and has operated flawlessly so far. This is mounted on one of my service trucks with a 40 gallon tank so it seems to run forever on a tank.

The Miller welders can provide lots of power but mine is too loud to use other than daytime.

The most quiet ones I have are the Honda 3000i and 200i inverter sets but their gas units and I agree it is safer to store diesel. The 2000i though at 47 #'s is by far the most convienient unit. If anyone is interested Honda has recently introduced a new 3000 w unit built like the 2000 and weighs in about 75 #'s, that would be a very handy genset to have. At 58 db these things are super quiet.

I expect the Aurora will use that under full load as well. I tested to see if it would run my 4.5KW Hot water tank and Well Pump at the same time and it did fine. That is what I was after with the upgrade fuel economy and the ability to have a hot shower. Honda is great equipment. The Diesel unit I have is not quiet it is the open frame but they offer a quiet model but I like the ability to easily service mine and the Quiet model was $400+ more.
 
/ Small diesel generators #22  
Yes, this one is a diesel, although they do sell gas-powered units too. This one will run about 4 hours on 1 gallon at less than 1/2 load, and is rated for 2 hours/gal at full load. The 6500W model is rated for 3 hours/gal at 1/2 load, and 1.5 hours/gal at full load.

As for the comment about Honda engines being made in China, from what I understand that is true, but they are built to Honda's specs, and subject to their inspection. The clones are not. The Chinese are master copiers. Most of the small gas powered engines coming from China are Honda knock offs, and most of the small single-cyl. air-cooled diesel coming from China are Yanmar knock offs. They see a good design and copy it.

Depending on your loads, you might want to look into the Honda or Yamaha inverter generators. Because they use an inverter, the engine doesn't have to run full speed regardless of load, so they use a lot less fuel at partial loads. They are a lot more money though.
Inverters are great but not all of them are created equal. The cheap one generate square wave, the better one generate modified sine wave (several square waves stacked on top of each other) only the best one generate good sine wave safe for your equipment such as electronics. Yamaha makes several of such models.
 
/ Small diesel generators #23  
Inverters are great but not all of them are created equal. The cheap one generate square wave, the better one generate modified sine wave (several square waves stacked on top of each other) only the best one generate good sine wave safe for your equipment such as electronics. Yamaha makes several of such models.

Both the Honda and Yamaha inverter generators are well regarded on the RV forums, and people that use them are running electronics with them.

Yes, you are correct, that all inverters are not created equally, but electronics (computers especially) will be fine with the MSW (modified sign) or even square-wave inverters. Most computers UPS's are MSW, and some are square wave. The switching power supplies in computers are fine with that.

The devices that are more sensitive to the "wave" type are motors. Induction motors will run a little hotter with MSW inverters, so you want to over size your inverter a bit when running MSW inverters with motors, to be sure you don't run them under voltage.

Xantrex makes inverters that can be "stacked" for 240V operation. I have two such units installed for emergency backup power. Each is rated for 3600W run power, and 7200W starting/surge power. Stacked, they give me 7200W run, 14400W surge. They use 24VDC input, and I have two deep cycle batteries powering them. They are charger/inverters with an automatic transfer switch, so I have my refrigerator, freezer, well pump (240V) and furnace all powered through them, so that they keep running when the power goes out. Because they are all intermittent loads, these two batteries can keep required things running through the night, so that I don't need to run generators over night. The other nice thing with this setup, is that in the summertime, it can probably run the refrigerator and freezer for a few days; longer if I add batteries. I also have transfer switches set up that I can power the entire house with the inverters to, so that I have lights (I run CFL's which use very little power).

For an extended outage, I can run the generator intermittently through the inverters to charge the batteries and run the house.
 
/ Small diesel generators #24  
I woulld point out that the Honda inverter gensets are quiet enough to run all night without being a problem. Next, the small Honda gensets have tiny gas tanks, a way around running out of gas is to buy a separate fuel cap and mount an outboard motor fuel connector to it so that you can use a 6 gallon portable tank with the generator. As the generator draws the fuel out of the built in tank it will siphon fuel from the auxillary tank which is the extended vent. Works like a charm and eliminates pouring and refilling hot gensets.
 
/ Small diesel generators
  • Thread Starter
#25  
Most of the US is in a deep freeze and it has been fairly cold here as well the temp the other morning was 8コF degrees and just for peace of mind I went out and tried to start the Chinese Yanmar clone genset. I hit the glowplugs for 20 seconds and turned it over and it fired right off. It run rough for about 30 seconds and then smoothed out. It has passed every test so far with flying colors.
 
/ Small diesel generators #26  
Sounds like a good unit. 8 degrees is a good starting test.
 
/ Small diesel generators
  • Thread Starter
#27  
I started my L4400 at the same time and the started about the same I didnt have the block heater plugged in either. Its supposed to get below 0コ this weekend around here so I will give it a shot again. I put 5W-40 Rotella Synthetic oil in the Genset after the 20 hour break in period.
 
/ Small diesel generators
  • Thread Starter
#28  
I think I have single handedly changed the weather patterns for my area of WV. Though we have had a few medium snows in our area we have not lost power 1 single time since I bought and broke in the diesel generator. All the ares around us have been hit by record breaking snows with extensive power outages but not me. Al Gore will be after me now for altering the weather with micro global (globelet) warming:D. Is any body interested in a weather changing diesel generator?:laughing::laughing::laughing:
 
/ Small diesel generators #29  
Same here. I bought a generator during an ice storm two years ago, and have since upgraded to a diesel unit. We haven't had a power outage longer than a few minutes since.
 
/ Small diesel generators #30  
I'm considering upgrading to a diesel unit for several reasons: 1) takes some cranking to start even though I run the carb empty after every run; 2) have to store volatile backup fuel; 3) need a bit bigger unit to put my well pump on without having to take everything else off line. This house once had a propane generator, but the seller took the generator with him but left the tanks and lines. I tore the lines out and had the tanks taken away. I worked with propane for 31 years and know it to be a very dangerous fluid (as is gasoline with its butane for starting). Natural gas would be great, but there's no line out here.

Has anyone used the 7000 watt diesel generators that Home Depot has for $1500? This is about the size to replace my 4400 watt gas unit. The gas unit uses 1/2 gallon/hr, and diesel will provide 50% less fuel consumption than a carbed gas engine. So, this 7000 watt unit would use about the same amount of fuel at full capacity.

Ralph
 
/ Small diesel generators #32  
I'm considering a 10KW PTO driven generator for my home.

Any idea about the fuel consumption for it running a 35 hp tractor? I imagine it will mostly be at idle speed.
 
/ Small diesel generators
  • Thread Starter
#33  
I'm considering a 10KW PTO driven generator for my home.

Any idea about the fuel consumption for it running a 35 hp tractor? I imagine it will mostly be at idle speed.

You will have to run your tractor at the RPM it takes to reach PTO speed. Most all of the commercially available generators have to run at 540RPM input to make the proper frequency (HZ) at the specific voltage. That said fuel consumption will be dependent on the load.
Running at full load you could expect approximately 0.75 gallon per hour.
Running at half load you could expect approximately 0.35 gallon per hour.
Lower than that load will not make much difference and these numbers will vary wildly sometimes dependent on the machine.
 
/ Small diesel generators #34  
/ Small diesel generators #35  
Well here is an update on the generator. ...snip...
I am going to hook up a power quality meter and see how much harmonic distortion is on the power from the generator.
Did you ever put a power quality meter on the generator? If so, how did it look? I am considering the enclosed unit, any guesses if the brushless generator would have any different (reduced) levels of distortion?
 
/ Small diesel generators #36  
Even cheap ($300) digital storage oscilloscope would do it. In example USB based box that you plug to your computer. You can observe the signal for some obvious distortion. Then switch to frequency analyzer mode and look for harmonic content. Pure sine wave has single frequency 60 Hz and none harmonics. The more harmonics you see and the larger is their amplitude the worse is the power. The advantage of power analyzer is that it will quantify it for you as opposed to scope that requires interpretation from acquired data.

While ago I watched few videos on YouTube. Some digitally controlled exciters did very poor job. The conclusion was that analog though not perfect were more consistent in providing reasonable power quality.
 
/ Small diesel generators #37  
My experience with the newer equipment in the last 10 yrs or so is the power has been much cleaner than I would have thought. Very easy to remember when running a generator was problematic. We had problems in town this weekend, one of my buddies and I looked at the incoming power on his Fluke 125 scope meter. It was so bad we shut everything down except a few light bulbs for about 5 hours.

While at his house we looked at the output of my Onan CMQD genset on the truck and found it to be clean. I also think the newer controls are alot faster reacting than years ago and are able to hold frequency dead on too. I would have liked to observe the output of my Honda's and Miller welder but maybe next time.

Most of the new consumer electronics can handle quite a bit of noise and distortion too, seems to filter it out remarkably well. You can use an inverter with a modified square wave output and get good results with a new tv or stereo . I was hesitant and a bit cynical about using a cheap inverter in my camper but it has done a good job so far. Can;t see any difference between running the powerline, inverter with batteries or Honda inverter genset they all give good results.
 
/ Small diesel generators #38  
I'm considering a 10KW PTO driven generator for my home.

Any idea about the fuel consumption for it running a 35 hp tractor? I imagine it will mostly be at idle speed.

My buddy, just had to run his PTO generator for several days, and he is not impressed. The power was good 12k pto gen, but the fuel consumption was more than he thought. He was using a 32 hp kubota. He also started to wonder about putting all those hours on his tractor. I would also point out that his unit cost around $1300. for a few hundred more, he could have gotten a stand alone, that his wife could have helped with. I have decided to go with a stand alone, after seeing what he went through.
 
/ Small diesel generators #39  
My experience with the newer equipment in the last 10 yrs or so is the power has been much cleaner than I would have thought. Very easy to remember when running a generator was problematic. We had problems in town this weekend, one of my buddies and I looked at the incoming power on his Fluke 125 scope meter. It was so bad we shut everything down except a few light bulbs for about 5 hours.

While at his house we looked at the output of my Onan CMQD genset on the truck and found it to be clean. I also think the newer controls are alot faster reacting than years ago and are able to hold frequency dead on too. I would have liked to observe the output of my Honda's and Miller welder but maybe next time.

Most of the new consumer electronics can handle quite a bit of noise and distortion too, seems to filter it out remarkably well. You can use an inverter with a modified square wave output and get good results with a new tv or stereo . I was hesitant and a bit cynical about using a cheap inverter in my camper but it has done a good job so far. Can;t see any difference between running the powerline, inverter with batteries or Honda inverter genset they all give good results.

Most consumer electronics have switching power supplies now. They care less about the quality of power. The transformer powered devices are much more sensitive.
 
/ Small diesel generators
  • Thread Starter
#40  
Did you ever put a power quality meter on the generator? If so, how did it look? I am considering the enclosed unit, any guesses if the brushless generator would have any different (reduced) levels of distortion?

Yes I did put the Fluke 434 power quality meter on the generator but it has been several months back. If I remember correctly the A harmonic distortion was 6%. Voltage and frequency was quit stable.


VOLTS WATTS RPM HZ
242V 0 3640 60.6
242V 100 3640 60.5
240V 1200 3616 60.3
240V 2700 3616 60.3
238V 4200 3598 60.1
236V 5580 3592 59.9
 
Last edited:

Marketplace Items

2013 Chevrolet Van (A55973)
2013 Chevrolet Van...
1977 Heil 6,300 Gallon T/A Tanker Trailer (A59230)
1977 Heil 6,300...
For Sale L4479 Snowblower and Subframe
For Sale L4479...
2003 Dodge Ram 4x4 Ext. Cab Pickup Truck (A59230)
2003 Dodge Ram 4x4...
2011 FORD F-550 (INOPERABLE) (A55745)
2011 FORD F-550...
2025 44in. HWG44 Hydraulic Mini Log Grapple Skid Steer Attachment (A59228)
2025 44in. HWG44...
 
Top