Ok perfect you have a lot of your info. The utility will pull 1 smallish wire to the transformer and then 3 large wires to your panel. You can do grounds outside. In that case it's 2 rods 8' long and 10'apart (verify distance). Those can be added later. I suggested the ufer as it's easier for most to just bury the rebar before you pour the concrete.
I want to make sure to provide good info here so let's make sure we all understand. The utility will install a transformer and then pull wires to the meter which is on the house? You are then wanting to take 200a to a guest house and 200a to the shop? Is this correct? The 3" you are asking about is the 200a leg to the shop? If that is the case 3" would work fine. You could run copper or aluminum THHN wire in that. In fact you could run smaller conduit if you wanted.
Interesting to note the utility is wanting 4"'conduit for the wires they are running....way oversized! They have much lower wire size standards and don't have to run 4 wires like you would.
I want to make sure to provide good info here so let's make sure we all understand. The utility will install a transformer and then pull wires to the meter which is on the house? You are then wanting to take 200a to a guest house and 200a to the shop? Is this correct? The 3" you are asking about is the 200a leg to the shop? If that is the case 3" would work fine. You could run copper or aluminum THHN wire in that. In fact you could run smaller conduit if you wanted.
Interesting to note the utility is wanting 4"'conduit for the wires they are running....way oversized! They have much lower wire size standards and don't have to run 4 wires like you would.