It won't. The GFCI trips when the current through the neutral isn't exactly the same as the current through the hot wire. Regardless of where the neutral is bonded to the ground, as long as it is upstream of the GFCI device all of the neutral current goes through the neutral on the GFCI. If the neutral touches ground downstream of the GFCI it provides a parallel path for some of the neutral current and will trip the GFCI immediately.
You are right.
It wasn't till the 2003 NEC ( maybe 2000) where it was required to run 4 wires to a separate building. For many years separate buildings had their neutrals bonded to the grounding electrode and the building's branch circuit equipment grounds. So, there was always current flowing through the ground rods and earth back to the premise service point.
Not a desirable situation, but certainly a common one.