OP here. It's a simple three zone system with a toggle switch for each zone and roughly 200 ft of wire to each zone including the common. I had checked the resistance through each circuit coming up with about 50 ohms on two circuits and about 30 ohms on the third which had the bad solenoid since replaced.
The solenoids are rated at about 0.4 amps inrush and about 0.25 amps holding current. (24VAC)
At this point I'm thinking it must be the nature of these transformers to run very hot since replacing a new one with another new one. I need to ask the supplier to talk to the manufacturer to see if that is the case.
Edit: Redneck in training suggested above that there could be a DC component in the primary causing the heat. Is there any way this can be verified with a VOM? I'm not aware of any DC devices in the vicinity.
The solenoids are rated at about 0.4 amps inrush and about 0.25 amps holding current. (24VAC)
At this point I'm thinking it must be the nature of these transformers to run very hot since replacing a new one with another new one. I need to ask the supplier to talk to the manufacturer to see if that is the case.
Edit: Redneck in training suggested above that there could be a DC component in the primary causing the heat. Is there any way this can be verified with a VOM? I'm not aware of any DC devices in the vicinity.