Hi Everyone,
I have been spending a lot of time this winter troubleshooting my heating system, and I may just have found something that needed correcting. I am in a new house, moved in last March, and the propane boiler shows 1863 hours of run time and 3300 cycles. In my opinion, this is excessive. I ran the heat last year for a few weeks, and this season I have had it on since the end of November. Boiler does gas cook stove and dryer, as well as domestic HW, but the domestic HW shows 47 hours of run time for 11 months that we have been here.I burned about 1.3 tons of coal too during this time. I hired the licensed Master Plumber because he was a neighbor, and I thought being neighborly was the right thing to do. When I talked with him about this, and other issues, he shouted repeatedly "It's not my fault, I am only 27". I may or may not deal with him through the licensing board but I don't know if I have the energy to fight city hall. Anyway, follow my story please.
The house is single story, full basement, 28 x 54, 2 x 6 walls with fiberglass insulation in all the right places. The heating system is propane fired Burnham boiler, header tank, domestic hot water tank, and two heating zones-- bedrooms (3) and living room, dining room, and kitchen. The boiler and trim is located on one end of the house, and a main supply and return passes through the center of the basement. Two Uponor manifolds supply the under floor tubing attached to aluminum heat plates. The manifolds are 3 place for the bedroom end, and 5 place for the main house. Each zone and the system has a Taco 3 speed circulator. I adjusted flow on the manifolds, and increased the temp on the bedroom manifold.As I was troubleshooting the system, I kept logs of run hours, outside temp, sun or clouds, just to get all the data I could.
I discovered that the bedroom zone seemed to run about 90% of the time, and the main house about 10%. The floors in the bedroom were warm, while the main house floors were always cold. The bedroom thermostat was always struggling to maintain 69 degrees, while the main house thermostat pretty pyramid much always read 70 degrees even though it was set at 69.
Here is what I found: the bedroom zone would run and run, and the heat passed out of the bedrooms through the hallway, and heated the house thermostat, which was at the point where the bedroom zone ended and the house zone began. It was like running a heating system with a window open. Said another way: the bedroom zone heated the bedrooms, but the heat continued through the hallway into the open living room, passing the living room t-stat on the way. So, the t-stat for the living room was not calling for heat, and the bedroom zone just kept running, never really catching up.
Here is what I did: unhooked the bedroom thermostat and just left the living room thermostat running. I wired the control box to control both zones at once. All manifold positions are full open, and both zones are set at 110 degrees. I tested this earlier today and it heated the whole house to 72 (from 69 degrees) in about an hour with the outside temperature in the low teens. I then lit the coal stove because it is going sub zero tonight for the next few days.
I think I may have finally fixed the problem. I did a heat loss on the house and boiler is sized large enough. We oriented the house westerly/southerly and used big windows so the boiler never runs on sunny days. As for the plumber, he is toast with me, I cannot believe he said "It's not my fault, I am only 27". I actually feel sick every time I think of that. In my day you stood tall and corrected your mistakes. I have already non recommended him for several jobs. Oh, and I did not get a bargain because he is young, just the opposite, he wants to be a millionaire by 30. Now I won't hire anybody under 35. Everybody else on this job, and we built it during the winter, was terrific. I know this post is lengthy, but folks here will offer guidance about this system.
I have been spending a lot of time this winter troubleshooting my heating system, and I may just have found something that needed correcting. I am in a new house, moved in last March, and the propane boiler shows 1863 hours of run time and 3300 cycles. In my opinion, this is excessive. I ran the heat last year for a few weeks, and this season I have had it on since the end of November. Boiler does gas cook stove and dryer, as well as domestic HW, but the domestic HW shows 47 hours of run time for 11 months that we have been here.I burned about 1.3 tons of coal too during this time. I hired the licensed Master Plumber because he was a neighbor, and I thought being neighborly was the right thing to do. When I talked with him about this, and other issues, he shouted repeatedly "It's not my fault, I am only 27". I may or may not deal with him through the licensing board but I don't know if I have the energy to fight city hall. Anyway, follow my story please.
The house is single story, full basement, 28 x 54, 2 x 6 walls with fiberglass insulation in all the right places. The heating system is propane fired Burnham boiler, header tank, domestic hot water tank, and two heating zones-- bedrooms (3) and living room, dining room, and kitchen. The boiler and trim is located on one end of the house, and a main supply and return passes through the center of the basement. Two Uponor manifolds supply the under floor tubing attached to aluminum heat plates. The manifolds are 3 place for the bedroom end, and 5 place for the main house. Each zone and the system has a Taco 3 speed circulator. I adjusted flow on the manifolds, and increased the temp on the bedroom manifold.As I was troubleshooting the system, I kept logs of run hours, outside temp, sun or clouds, just to get all the data I could.
I discovered that the bedroom zone seemed to run about 90% of the time, and the main house about 10%. The floors in the bedroom were warm, while the main house floors were always cold. The bedroom thermostat was always struggling to maintain 69 degrees, while the main house thermostat pretty pyramid much always read 70 degrees even though it was set at 69.
Here is what I found: the bedroom zone would run and run, and the heat passed out of the bedrooms through the hallway, and heated the house thermostat, which was at the point where the bedroom zone ended and the house zone began. It was like running a heating system with a window open. Said another way: the bedroom zone heated the bedrooms, but the heat continued through the hallway into the open living room, passing the living room t-stat on the way. So, the t-stat for the living room was not calling for heat, and the bedroom zone just kept running, never really catching up.
Here is what I did: unhooked the bedroom thermostat and just left the living room thermostat running. I wired the control box to control both zones at once. All manifold positions are full open, and both zones are set at 110 degrees. I tested this earlier today and it heated the whole house to 72 (from 69 degrees) in about an hour with the outside temperature in the low teens. I then lit the coal stove because it is going sub zero tonight for the next few days.
I think I may have finally fixed the problem. I did a heat loss on the house and boiler is sized large enough. We oriented the house westerly/southerly and used big windows so the boiler never runs on sunny days. As for the plumber, he is toast with me, I cannot believe he said "It's not my fault, I am only 27". I actually feel sick every time I think of that. In my day you stood tall and corrected your mistakes. I have already non recommended him for several jobs. Oh, and I did not get a bargain because he is young, just the opposite, he wants to be a millionaire by 30. Now I won't hire anybody under 35. Everybody else on this job, and we built it during the winter, was terrific. I know this post is lengthy, but folks here will offer guidance about this system.