My service entrance conduit had to be "below" 5 feet, or "over" 5 feet deep. It had to have a pull box every 100' and mine was 220 feet to the pole so I had two. The 90s at the ends are long radius sweeps. All above ground service entrance conduit must be either schedule 80 PVC or rigid metal conduit. No EMT thinwall metal conduit. No EMT below grade in the ground. So, the main runs can be sch 40 but must switch to heavier grade where they turn up. My utility wanted a pull rope installed and some even want the official thing (can't remember the name) pulled through to prove the conduit is clear. At approximately one foot above the conduit an official 6" wide red caution tape must be run to warm of the conduits location. If the ditch is to be used for other lines, like water for instance, they should or must be at least one foot apart.
All this is for the main service conduits. The secondary conduits that run to sub panels or from the meter to the house, can be at 24 inches. But mine are deeper because they run with water lines and I needed at least three feet for those to prevent freezing.
Always run a big enough size! Larger means a much easier pull, less chance for wire damage and the chance to get another wire through if needed. Bigger is better!
I was concerned about settling and stress on the box so I just filled it slowly and washed it in with water to compact it without downward pressure. No other special design was used. We don't get heaving here and the initial settling was handled by washing it in for compaction. The conduit comes up to a male thread coupling and a nut in the box.
You also can't have more than 270 degrees of bends in each run of conduit. But the casual bending in the ditch doesn't count.