14 gauge in this example might technically meet the ampacity requirement of the Code, but also the voltage drop must be considered. For example, a receptacle that's only 10 ft from the breaker would have very little voltage drop, but a receptacle 150 ft away likely would have excessive voltage drop, in which case the wire size should be increased (say from 12 ga to 10 ga). There are calculators online that will calculate the acceptable voltage drops for different combinations of lengths, current, and wire size.