What voltage does your generator run at?
   / What voltage does your generator run at? #51
Motors have starting and running capacitors to compensate for phase shift.
Actually motors use capacitors to produce a phase shift, not correct it. The phase shift is needed to start the motor, or increase starting torque, and increase torque under load.
Also stated earlier that capacitors are used by utilities to increase voltage is also not correct. The capacitors are to improve power factor, which is in simple terms bringing voltage and current closer into phase with each other.
Watts = Volts x Amperes x Power factor (true power). Volts x Amperes are known as VA. You will see most generators will have a Watt and VA rating, which are rarely the same.
Paul
   / What voltage does your generator run at? #52
The phase shift during starting is momentary. As for power factor correction while running? Close enough is considered good enough, with 0.90 PF is usually the closest to unity with the exception of window airconditoners which are close to 1.0 PF to eliminate lagging reactive current from circulating through the supply breaker . Leaving the breaker's current capacity to perform work instead of circulating reactive power that loads components but performs no work.
Well I got around to setting the Gillette generator. I found a manual online that said to set speed of the engine so the voltage is 124V and frequency 62. I set the mechanical governor to get 124V and the frequency read 63 on my Fluke. It doesn't have any adjustment other than the governor. I'd like to test it under load and I'm thinking electric space heaters would be easy.
   / What voltage does your generator run at? #54
The power grid is running about .85
Capacitors are for starting, not power quality. You have no idea what you are talking about.
You need to learn about vars.
   / What voltage does your generator run at? #55
Paul
Capacitors raise voltage. You know a little.
Power companies charge for watts not vars. But they cannot change your consumption .
During the day transformers raise taps to keep voltage up. They will also switch in caps. At a big city they may have genetation export vars or try correct power.
Caps are vars one way inductors are the other.
You can take 600v inductive furnace, around pf. 3 and add caps to bring it up 1400 v, and .9 pf.
   / What voltage does your generator run at? #56
I don't work with little stuff. 63 hertz to me sounds like an awful governor. But it may not be. It may be typical.
Your load will drag it down. But it is at 63 when.lightly liad r c I take it. The grid is at 59.999. 59.997 will start shedding g load. But it may not matter at your house. You are doing an open change over.
I would be curious what other generators do. Your house as an island is a lot different. They are concerned about a load dragging it down.
Years ago I said buy this generator kw was enough. They started a small garage size air compressor and it didn't like it.
   / What voltage does your generator run at? #57
What is little stuff?
The generators at work put out 12470 volts, two at 1825 KW and one at 3165 KW :shocked:
   / What voltage does your generator run at? #58
   / What voltage does your generator run at? #59
Small stuff.
It is not so much the voltage. 600 MW generators, generate at 13kV.
I have worked with 2MW diesels cats. Nice back up generation. Little hydros and some tiny steam is under 3MW too.
   / What voltage does your generator run at? #60
The math is easy... Volts x amps = watts...
SO, 220 volts x 4.8 amps = 1,056 watts...
SR
This works for heaters, not motors.
Motor name plates have pf. Think of it kinda like efficiency. 1 is best. Divide by .85 or pf to get amps.
Google power triangle. Right triangle. resisistance, it is just a line, 0 degrees, pf 1. Watts = Volt Amps, VA. Inductors and caps add to the vertical legs, one up,one down, opposite. VA gets bigger, hyptoneuse, watts get smaller, adjecent. zero angle hyptoneuse equals adjacent. Vertical = horizontal leg of right triangle.
Transformers are rated in VA. You should do all your panel and service sizing in VA. Heaters and lights bulbs, are about the only thing measured only in watts. Everything else has an inductive or capacitive portion.
Since the hypotenuse is getting bigger so are the amount of amps. Flat line, zero degrees, less amps. Voltage is constant.
2022 John Deere Z930M (A57148)
2022 John Deere...
LIKE NEW 2023 Rhino 84in Reverse Rotation Rotary Tiller (A56436)
LIKE NEW 2023...
2024 CATERPILLAR 305 CR EXCAVATOR (A52709)
2024 CATERPILLAR...
2020 CATERPILLAR 306 CR EXCAVATOR (A60429)
2020 CATERPILLAR...
INTERNATIONAL DUMP TRUCK (A52707)
INTERNATIONAL DUMP...
INGERSOLL RAND  G25 GENERATOR (A58216)
INGERSOLL RAND...