"Is there EVER a situation where it is legal to run a 10 gauge wire into a 60 amp breaker?
Yes, For the Rating of individual motor circuits, Article 430.52 in the NEC states that when using an inverse time circuit breakers to use 250 percent of the full load current. example; 24 amps of calculated full load motor current multiplied by 2.5 (250 percent) equals 60 amp inverse time circuit breaker.
The heat pump or air conditioner should have the fuse/breaker size you should use on a label fastened to the unit.
Refrigeration equipment Circuit breakers have a multiplier of 1.75 (175 percent of current rating). If the 175 percent can't start the load without tripping you can use up to 225 percent of rated motor current to size the breaker.
Yes, For the Rating of individual motor circuits, Article 430.52 in the NEC states that when using an inverse time circuit breakers to use 250 percent of the full load current. example; 24 amps of calculated full load motor current multiplied by 2.5 (250 percent) equals 60 amp inverse time circuit breaker.
The heat pump or air conditioner should have the fuse/breaker size you should use on a label fastened to the unit.
Refrigeration equipment Circuit breakers have a multiplier of 1.75 (175 percent of current rating). If the 175 percent can't start the load without tripping you can use up to 225 percent of rated motor current to size the breaker.