MossRoad said:Rob,
You could just put an on-off-on switch between your meter and main panel with the first ON being your electric company power, the OFF to isolate the two services, and the second ON being your generator. Then you manage the load with your breakers. This method takes the least amount of wiring, is most likely code legal as the two power sources cannot be mixed, and probably the cheapest in the long run, although you will be shocked at the price of an on-off-on switch at first. But the ease of installation and no need to pull circuits from existing panels may make it more attractive.
Mossroad
A manual transfer switch placed between meter and panel is probably the most expensive option of any discussed here... To install it, you have to have the meter pulled to access and replace the conduit and wiring between meter and main panel and locate the switch in a reachable location. A liscensed electrician will most likley have to do the final wiring, or at the very least you will be paying for him to come and sign off on it, so it can pass an inspection before the local utility will re-install the meter. This is the same as if you had a new main panel installed. The prices of a 2 pole switch capable of switching several hundred amps current capacity(has to handle your normal commercial capacity, so 200+ amps)are also WAY up there. If I was going to do a whole house backup generator, then sure why not. But that is a huge investment for a 5KW emergency generator.
In all of my research(over the past several years), the main panel interlock kits, at around $150, are the least expensive UL approved method of adding hard wired manual control backup power that I have come across. The backup-ready main panels with the interlock plate already installed are starting to be quite common on the shelf in the bigbox and electrical supply stores. The kits are also no more difficult to install than installing a new circuit breaker into the panel. You shutoff the main, remove the cover plate and remove the top right 240 breaker. You relocate it and it's wireing to an open slot down lower in the panel. You install a new 240 breaker sized for your generators capability into that top right slot and wire the generator hots to that. the generator neutral and ground go to the main panel busses just like the commercial powerlines do. You then drill the panel cover plate with a template and rivet the interlock plate in place. Once the panel coverplate is re-installed, the main breaker and top right generator breaker can't physically be on at the same time...