Yes should have only 1 (one) Neutral to Ground Bond and that should be at the Main Panel or Service disconnect switch or meter (but not at all 3).
Whether to drive another ground rod or connect to the rebar or mesh in the concrete? You will probably get a better ground (lower impedance to ground) by connecting to the Rebar or mesh. Concrete is conductive and actually makes a pretty good ground system (usually better than a couple of 8' rods). The Concrete Encased Ground Electrode or Ufer Ground (named after the guy that researched them for the Army back in the 50s?) has been found to provide much better grounds than other methods for certain soil conditions.
NEC (National Electric Code) now calls for all sub panels to be fed with 4 wires (Hot-Hot-Neutral and Ground) and you need to make sure that the Neutral and Ground are separated at the sub-panel(s) (remove the bonding screw or strap). Barns (if I remember correctly) have some unique grounding requirements under the code as stock can feel ground potential diffences that people can not (front and back feet are separated by a distance and so they pick up more of the voltage/potential difference than we can -- unless you can separate your feet that far), not to mention that most barns have manure/mud mixtures in or near them that are very conductive.
Let me know if you have further questions.
Yes should have only 1 (one) Neutral to Ground Bond and that should be at the Main Panel or Service disconnect switch or meter (but not at all 3).
Whether to drive another ground rod or connect to the rebar or mesh in the concrete? You will probably get a better ground (lower impedance to ground) by connecting to the Rebar or mesh. Concrete is conductive and actually makes a pretty good ground system (usually better than a couple of 8' rods). The Concrete Encased Ground Electrode or Ufer Ground (named after the guy that researched them for the Army back in the 50s?) has been found to provide much better grounds than other methods for certain soil conditions.
NEC (National Electric Code) now calls for all sub panels to be fed with 4 wires (Hot-Hot-Neutral and Ground) and you need to make sure that the Neutral and Ground are separated at the sub-panel(s) (remove the bonding screw or strap). Barns (if I remember correctly) have some unique grounding requirements under the code as stock can feel ground potential diffences that people can not (front and back feet are separated by a distance and so they pick up more of the voltage/potential difference than we can -- unless you can separate your feet that far), not to mention that most barns have manure/mud mixtures in or near them that are very conductive.
Let me know if you have further questions.