I was required to put a ground rod at the sub-panel in the garage, too.
BEEZs
The issue is if you run a wire 1000 feet away then connect only the ground wire back to the main panel in the house you have a LOT of potential ground difference in the earth between the two buildings. If you are standing on dirt or concrete (typical floor in an out building) and plug in a drill & stand on the wet floor you have a high chance if a great voltage difference between the GROUND of the CASE of your drill and the DIRT under your feet. That means you CAN get shocked even from the GROUND SYSTEM not just the Conductor or Neutral system! That is why you have to tie the ground rods to the sub panel of the panel but not the neutral of the sub panel. It ties the grounds all together but depends on the insulated/coated neutral wire to carry all of that normal current back to the main panel. The often bare ground wires then are simply keeping all the earth local potential to the main earth.
Mark
I just had a similar installation done, both the electricians who did the work and the county said that ground rods weren't allowed at the barn. The ground wire from barn had to be carried back to the house and connected to main panel ground bar. The explanation was that the ground rods can be at different potentials because of different soil conditions or corrosion in connections. That can create ground loops that affect electronics equipment, particularly audio and video, and make it possible for the grounded case of electrical equipment to give someone a small shock. I have no idea if this is some local thing, or an NEC thing.
I was required to put a ground rod at the sub-panel in the garage, too.
Good Afternoon Beezfun,
" I have no idea if this is some local thing, or an NEC thing."
I am far from an electrician, but when I built my barn a few years back, I ran 150 ft of cable out to the 100 amp sub panel in the barn and used two copper grounding rods outside the corner of the building. So far everything has worked fine, no issues.
My best guess is this is a local code issue in your area !
I thought about it for a second. Glad the inspection is done. Part of the problem is in your question.
A barn or out building is not a sub panel but rather its own service, even if served from your house. So don't remove the neutral to ground strap (jumper). Because the barn is its own service you need another ground source. Here that would mean a ground plate or two driven ground rods, this can be different in different jurisdictions.
For clarity, a sub panel would be in the same building. In a sub panel is where you remove the neutral to ground jumper as you only ground your neutral once per service.
I realize it's a play in n words but it's similar to ground and bond, totally different but still the same.