alexpops
Platinum Member
Not to highjack the thread, but for the guys that do (have done) this for a living, when calculating distance for voltage drop, is it linear distance from source panel, or do you double that for the length of the circuit?
You dont know what your talking about. Each leg carries 30 amp.When running 240vac the current load is shared by both hot legs so factor that into your wiring choice. For example if welder pulls 30 amps each leg supplies 15 amps so wiring can be determined by that and wire run length.
wire it and use welder for 240vac and forget about using it with 120vac IMO.
39? Typo?You dont know what your talking about. Each leg carries 39 amp.
nothing like the internet to pass on wrong info.
I was going by the Cerrowire chart.
I’d use 6 ga in Romex, but if I’m reading the chart right, I could use 8ga 90C THHN in EMT up to 55 A. Wouldn’t run a continuous load like a Tesla charger off 8ga, though
Copied and pasted from the bottom of the chart in the link.I was going by the Cerrowire chart.
I’d use 6 ga in Romex, but if I’m reading the chart right, I could use 8ga 90C THHN in EMT up to 55 A. Wouldn’t run a continuous load like a Tesla charger off 8ga, though
Thanks. I have an older copy of the NEC. Be interested in the 60C citationCopied and pasted from the bottom of the chart in the link.
WARNING! Installation of electrical wire can be hazardous if done improperly, and can result in personal injury or property damage.
For safe wiring practices, consult the National Electrical Code ®, your local building inspector, or a qualified electrician.
#8 THHN is only rated for the ampacity in the 60°C column due to a code requirement in article 110 of the NEC. It would be good for ampacity of up to 40 amps according to the ampacity table in the attachment.