RonMar
Elite Member
You guys missed the question that I asked.
No we didn't. What part of hardwire the generator, or replace the 50A receptical and plug with a larger one didn't you understand?
Ok, to elaborate, you said the generator has a 50A 240V receptical. Well somewhere inside that junction box is 63A of capability that feeds the 240V and 120V recepticals. If the installed 50A receptical won't cut it for your single connection, you will have to dig into the box and bypass the factory receptical. IE, hardwire from this higher capacity point inside the generator junction box to your transfer switch, or put in a larger capacity receptical that connects back to that 63A of capability.