electrical requirements for Miller 211

   / electrical requirements for Miller 211 #11  
The idea is that you should not load a circuit to more than 80% of the breaker rating in other words, a 20 amp breaker should not be continuously loaded over 80% of 20 amps or 16 amps. The exception here is "continuous load". Loading a 30 amp breaker to 24 amps is fine for a welder because I know the duty cycle on the welder you have is not 100% and thus the wire has a cooling period
Your welder has a duty cycle that does not allow it to be continously loaded. Duty cycle plays a role in selecting wire size, its not always just the breaker. A good example of this is the HVAC circuit on your home that runs the compressor, rarely does the wire size match the breaker size, that is, 12 gauge/20 amp 10 gauge/30 amp etc. If you have a 30 amp 240V circuit using number 10 wire, you have the built in assurance you need that the wire is protected. Remember that you rarely weld at the top of current range and on many welders, your duty cycle is reflected by this. It gets complicated, people here always simplify it to wire size to breaker size must match but that is just not the case. That being said, it will less likely result in a fire when you oversize the wire and when that wire is protected by a suitable size breaker.

For your reading fun; http://books.google.com/books?id=8c...duty+cycle&source=bl&ots=2bgqjM8WlG&sig=q9i14

Herein lies the problem. I am using this welder in a friend's garage. He has a230 V outlet there for occasional use. I need to verify the breaker size, but I assume it is a 30A. The existing outlet obviously doesn't mate with my Miller welders plug. Since I am borrowing his space, I am not at liberty to rewire his garage ideally. I can always use it at the 120V mode there, but would rather have the increased power of 230V if it can be done safely.

Could I run this welder off a 8000 W generator? My generator has a 230V outlet, 30A locking plug style. Same question, if so, how do I plug it in?
 
Last edited:
   / electrical requirements for Miller 211 #12  
why not just swap his 240v receptacle with yours while you are using the shop and then swap it back when you are done?

how long does it take to re and re 4 wires?

120v is a joke.
 
   / electrical requirements for Miller 211 #14  
Somewhere in this thread, the OP said that the owners manual stated that the MAXIMUM size fuse or breaker to use was 30 amps so he has a 30 amp breaker which is the max needed. Get a male plug to match the receptacle you want to use and put it on your power cord and start welding. I would avoid adapters and such as many of those will overheat and you really dont know what they have used to make them. Dont overthink the situation with the supplied plugs, disregard the plug issue furnished with the machine. GO with the rating that is specified and put on a 30 amp plug to fit the source and you will have no problems. If the breaker should trip, then it is doing its job, protecting the wiring and your machine, but I dont think you will have an issue with tripping on that machine.
 
   / electrical requirements for Miller 211 #15  
I agree Gary. The one thing about welders is the huge benefit you get from the user not welding non stop for hours on end. Its not like your running an electric heater for hours or more non stop where the wires supplying the current never get a chance to cool. That is a situation where you must always provide 100% sizing from the wire size chart. What I am curious about after visiting the Miller site is why he does not just use the MVP cordsets that were provided.


Somewhere in this thread, the OP said that the owners manual stated that the MAXIMUM size fuse or breaker to use was 30 amps so he has a 30 amp breaker which is the max needed. Get a male plug to match the receptacle you want to use and put it on your power cord and start welding. I would avoid adapters and such as many of those will overheat and you really dont know what they have used to make them. Dont overthink the situation with the supplied plugs, disregard the plug issue furnished with the machine. GO with the rating that is specified and put on a 30 amp plug to fit the source and you will have no problems. If the breaker should trip, then it is doing its job, protecting the wiring and your machine, but I dont think you will have an issue with tripping on that machine.
 
   / electrical requirements for Miller 211 #16  
If this is true then I am converting everything to 240V including the clock radios. If I go to 480V do I save even more on power? How about right off the pole?

I'll assume a given device consumes 1200 watts, a hair dryer for example.

12000 volts x .1000 amps = 1200 watts

480 volts X 2.5 amps = 1200 watts

240 volts X 5 amps = 1200 watts

120 volts X 10 amps = 1200 watts

Dang, its still not true


Quote:
Originally Posted by Sumpter
.... and 220 is always better than 120. It is also cheaper in the long run. Less amps are used which mean less power used.

I certainly hope that this statement was a senior moment. :(
 
   / electrical requirements for Miller 211 #17  
.... and 220 is always better than 120. It is also cheaper in the long run. Less amps are used which mean less power used.

so you may use just as many amps (overall) with 240v, but being able to distribute the load must result in some cost savings? it certainly makes the physical wiring task a lot easier, not to mention the difficulty of trying to find a 20a/120v plug that will fit into a 20a/120v receptacle. the 90* spade is always on the wrong side:confused: in fact i have been to home depot and the receptacle doesn't match the plug there either.

i have never had anything but bad luck trying to weld with 120v. i have a 120v 'stick' machine that i bought at canadian tire, paid $100.00, it's utterly useless... that i would happily take $5.00 for just so as not to have to fess up that i paid $100.00 for it and ended up taking it to the dump.
 
   / electrical requirements for Miller 211 #19  
How did you plug in your Miller 255 MIG into a 30 amp circuit? That is my confusion.

Simple. I just made an extension cord that plugged into the 30 amp outlet that I could plug my welder into. Since the garage was detached from the house and was wire with two lines going to it, a 20 amp 110 line and a 30 amp 220 line it would have required digging up a patio and running new cable to put anything bigger in. The house only had 100 amp service and had an odd ball panel so that would have needed replacing as well since the only breaker that was rated above 30 amps was for the electric drier.

At first I monitored the current but when it never reached 30 amps I just counted on the breaker doing it's job.
 
   / electrical requirements for Miller 211 #20  
220 is always better than 120. It is also cheaper in the long run. Less amps are used which mean less power used.
\

Like the others are saying, you don't pay for amps used, you pay for watts.
 

Tractor & Equipment Auctions

2015 CATERPILLAR 259D SKID STEER (A51242)
2015 CATERPILLAR...
Woods LR72 72" 3pt Rake (A50774)
Woods LR72 72" 3pt...
2022 Case IH Steiger 470HD AFS Connect RowTrac 4WD Tractor (A50657)
2022 Case IH...
2023 KOMATSU WA480-8 LOADER (A51242)
2023 KOMATSU...
2015 JOHN DEERE 624K WHEEL LOADER (A51406)
2015 JOHN DEERE...
2015 Mitsubishi Mirage Sedan (A50324)
2015 Mitsubishi...
 
Top