The idea is that you should not load a circuit to more than 80% of the breaker rating in other words, a 20 amp breaker should not be continuously loaded over 80% of 20 amps or 16 amps. The exception here is "continuous load". Loading a 30 amp breaker to 24 amps is fine for a welder because I know the duty cycle on the welder you have is not 100% and thus the wire has a cooling period
Your welder has a duty cycle that does not allow it to be continously loaded. Duty cycle plays a role in selecting wire size, its not always just the breaker. A good example of this is the HVAC circuit on your home that runs the compressor, rarely does the wire size match the breaker size, that is, 12 gauge/20 amp 10 gauge/30 amp etc. If you have a 30 amp 240V circuit using number 10 wire, you have the built in assurance you need that the wire is protected. Remember that you rarely weld at the top of current range and on many welders, your duty cycle is reflected by this. It gets complicated, people here always simplify it to wire size to breaker size must match but that is just not the case. That being said, it will less likely result in a fire when you oversize the wire and when that wire is protected by a suitable size breaker.
For your reading fun; http://books.google.com/books?id=8c...duty+cycle&source=bl&ots=2bgqjM8WlG&sig=q9i14
Your welder has a duty cycle that does not allow it to be continously loaded. Duty cycle plays a role in selecting wire size, its not always just the breaker. A good example of this is the HVAC circuit on your home that runs the compressor, rarely does the wire size match the breaker size, that is, 12 gauge/20 amp 10 gauge/30 amp etc. If you have a 30 amp 240V circuit using number 10 wire, you have the built in assurance you need that the wire is protected. Remember that you rarely weld at the top of current range and on many welders, your duty cycle is reflected by this. It gets complicated, people here always simplify it to wire size to breaker size must match but that is just not the case. That being said, it will less likely result in a fire when you oversize the wire and when that wire is protected by a suitable size breaker.
For your reading fun; http://books.google.com/books?id=8c...duty+cycle&source=bl&ots=2bgqjM8WlG&sig=q9i14
Herein lies the problem. I am using this welder in a friend's garage. He has a230 V outlet there for occasional use. I need to verify the breaker size, but I assume it is a 30A. The existing outlet obviously doesn't mate with my Miller welders plug. Since I am borrowing his space, I am not at liberty to rewire his garage ideally. I can always use it at the 120V mode there, but would rather have the increased power of 230V if it can be done safely.
Could I run this welder off a 8000 W generator? My generator has a 230V outlet, 30A locking plug style. Same question, if so, how do I plug it in?