I've got a huge job coming up, and I could use advice on technique.
After years of petitioning, the Power Company has consented to provide electricity to my isolated acreage in the VA mountains.
I have agreed to trench 36" underground from my service drop location to the nearest power pole, and put in 3" conduit with pull rope so that when the Power Co comes, they only need to pull the main feed (600A) cable from the nearest pole to my service drop.
Here's what makes it interesting: This is not going to be like pulling Cat5 through 40-50 feet. It's going to be a 1500 foot-long distance. With BEEG honking cable. Power Co has to pull the cable (thank Dog) but what is the best way to set up rope to pull through 1500 feet of 3" schedule 40 electrical conduit in a trench?
How do the pros do this? In 30 50-foot segments? 15 100-foot segments? Clearly I can't get a 1500 foot rope (and if I could, can you imagine trying to pull a cable that big that far? Ay yi yi...)
If I want the PowerCo guys to be able to work uninterrupted, do I need 30 50-foot ropes? What seemed conceptually simple (how hard can it be, you thread rope through a 3" pipe) becomes not so simple when I get to the details.
Who's been there? What's the right way to do this (besides subbing the job out)? I'm all ears, friends. Can you help me figure this one out?
Before this snake gets out of hand you are going to have to rethink the entire issue!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
You will need a 600 foot spool of pulling rope and a cable puller if you can rent one as they will charge you for it anyway.
Assuming you will be coming down from 4,000 volts single
phase to 220 volts single phase.
1/0 gauge or 2/0 guage 600 amphere feeder line wire with ground.
A three wire strand with 2 insulated conductors for the hot and neutral legs and a bare aluminum coated copper ground cable as line wire number three.
At the least you will need three junctions at 500 foot intervals to pull the 3 wire feeder cable.
The trench will have to be widened to allow room for the winch and the labor
at the junctions.
You also have to leave the trench open for the inspector before and after the pulling job is done.
You will either have to have/own a 600 foot wire tape or hire a contractor that can fire a projectile/ pipe ball throught the conduit to the open end at 500 feet to allow pulling a wire tape after the ball pulls the nylon twine through and then a cable pulling rope and then a Kellums clamp to secure the wire bundle in the conduit to pull it through.(also known as a chinese finger puzzle)
You will also need a substantial amount of cable lubricant being 5 to ten gallons or more in pails to do this as well as the smallest amount of damage on the insulation jacket will affect the cables ability for winching.
Your looking at 20.9 percent voltage drop with a 600 volt 100 amp circuit alone!!!!!!!
I think you should seriously think about having a transformer and a few poles added to this mess to avoid the line drop issues.
Otherwise the only economical method is high amperage locomotive sized storage batteries from DEKA and a generator with or without solar panels which will cost you less money to begin with.