My problem here is that I do not know enough about what is proper. For instance, can I use a 50 amp breaker on #10 wire? Someone here did but I would never had guessed it as appropriate with all the warnings I've heard about undersizing wiring with a larger breaker. The irony here is that I've been around welders my entire life. Its just that I never was the one fixing something on a skidder or excavator so I never paid much attention. Plus, these were massive welders on a truck driven by also large generators. That is why I needed someone with experience to say "get this and you'll be ok to do what you want" For the welding I have done and for the welders I've used. I am not a fan of ac welding. 7014 rod makes ac a lot easier for me but even a friends 220 volt Hobart stick with 6011's still stuck rods. Never welded with dc hence my query on inverters and hearing their loads are easier, thought they would fit the bill. As I said, don't know enough even going thru all the old posts in the welder section.
Legally...NO you cannot use a 50 amp breaker on #10 wire. At best #10 can handle 40 amps, But the NEC also stated that it cannot be fused greater than 30 amps by convention. When some people run a #10 to a 50 amp circuit there using a derate allowed for welders. However the 50 amp receptacle IS wired with #6 (or appropriate sized) wire to the 50 amp breaker. There using a short (not 50-70') extension cord of #10 to plug into the 50 amp receptacle.
Other factors come into affect with long runs of what is basically extension cord....namely voltage drop.
Buying a 50 foot run of heavier cord isn't really that expensive. I have a 50 foot run of #6 SO cord for my wiggle box, and boy it sure comes in handy.