electrical/ pressure switch question

   / electrical/ pressure switch question
  • Thread Starter
#31  
Have you verified with tester at above mentioned box that in fact current cycles with pump or is this an assumption, just trying to pinpoint.
It i pretty much a fact since the lead from the panel inside my house runs through my pressure switch and then down to the breaker box in the field.
 
   / electrical/ pressure switch question #32  
It i pretty much a fact since the lead from the panel inside my house runs through my pressure switch and then down to the breaker box in the field.

It would appear then if you want a constant electrical supply at pond, the only way to accomplish without a home run from the panel is to relocate the pressure switch.
 
   / electrical/ pressure switch question #33  
I have terrible well water , full of iron. but, I also have a creek that originates on my property so, I put a 220v submersible pump into the creek, then all the required filters on it and now i have wonderful water.

I obviously ran 220v wire ( 8/2 I believe it was) 500ft to my creek for the pump. I also have a very nice large pond that we use for hanging out and swimming in the summer. I would like to have electric down by the pond. So, I put a breaker box in halfway down my field to split off the 220v for the pump. I had an electrician wire it up so now I have a 220v breaker and a 120v breaker in the breaker box. I have yet to run the 120v wire to the pond.

But then I realized that the only time I will get power to my 120v outlet by the pond will be when the pressure switch is closed and calliing for water to my house.
how can I solve this problem without running ery expensive wire 500ft again? Maybe put the pressure switch after the filed breaker box somehow????/

Like others have said run a new wire and the life you save might be your own,, Stop trying to make it work the facts are your "electrician ?" made a mistake. You can not do what you want with the wire that you have,, Not by changing to 120v pump and not by jumping this or moving that.. You say no codes there.. Well they are called "Life saftey codes" for a reason.. Do you have kids.. Then do it for them.. :D
 
   / electrical/ pressure switch question
  • Thread Starter
#34  
Like others have said run a new wire and the life you save might be your own,, Stop trying to make it work the facts are your "electrician ?" made a mistake. You can not do what you want with the wire that you have,, Not by changing to 120v pump and not by jumping this or moving that.. You say no codes there.. Well they are called "Life saftey codes" for a reason.. Do you have kids.. Then do it for them.. :D

Now I know what codes are for..... thanks.
 
   / electrical/ pressure switch question #35  
Like someone else has said, are you sure you don't have power. He may have done what I was trying to explain. One question, do you have a control box after the switch? It will have red yellow and black strand wire coming out going to the pump.
 
   / electrical/ pressure switch question
  • Thread Starter
#36  
Like someone else has said, are you sure you don't have power. He may have done what I was trying to explain. One question, do you have a control box after the switch? It will have red yellow and black strand wire coming out going to the pump.

I know I don't have power. I recently switched out the pressure switch and the way it is wired it is easy to see that it does not have power.
Nope , no control box, It is a two wire pump.
 
   / electrical/ pressure switch question #37  
8 2 romex does not have a neutral. it will only have 2 hots and a ground wire

I doubt there's any such thing as 8/2 Romex. He probably has 8 gauge pump wire, which is 2 hots and a neutral, no ground. Running a ground hundreds of feet is not a good idea, since you can have a local potential on a remote ground. The junction box needs to establish a local ground. In the old NEC, the neutral and ground were bonded at the remote box. That changed and more ground wires were run to separate buildings, but for farm use a local ground is the only way to go.
 
   / electrical/ pressure switch question #38  
but, SInce i already fried my pump. I was thinking of a 110v jetpump of some sort inside a heated little shed down by the creekbed. Has anyone used a jet pump outdoors in a cold region?

Small pumps are OK, but you should run even a small pump on 240v. That cuts the amperage in half, and you will get much better pump life from the higher voltage. Every water pump I have ever seen gives directions for switching the motor from 120 to 240v.

Even in a pit, you are going to have to have heat tape or something similar. There are thermo-bricks that turn on at 35 degrees, so put one next to the pump and when it is in danger of freezing the heat will kick on.
 
   / electrical/ pressure switch question #39  
I doubt there's any such thing as 8/2 Romex. He probably has 8 gauge pump wire, which is 2 hots and a neutral, no ground. Running a ground hundreds of feet is not a good idea, since you can have a local potential on a remote ground. The junction box needs to establish a local ground. In the old NEC, the neutral and ground were bonded at the remote box. That changed and more ground wires were run to separate buildings, but for farm use a local ground is the only way to go.

what are you talking about???

i use miles of 8/2 and 8/3 romex with ground. for undergrund its called UF cable . Alot of people refer to it as burial romex.

whats in a name.


i know what your referring to with the pump wire, we have it here and its run in a twisted bundle of 4 wires.

The code requires a ground run between a main panel and a subpanel. if this is work done in the past 3 years then its not done right. If indeed it is romex run between the panel then the wire being used for a neutral is bare copper, and cannot be used as a neutral wire (which can and does conduct power.
 
   / electrical/ pressure switch question #40  
Not sure how my electrician wired it really. i just drew the pic.

Moving the tank and/or anything that holds water above ground outside is not an option. it gets well below zero at my place. Looks like I am running more wire !


Moving the tank or anything from original would NOT be a good idea. If something happen, you will pull all your hair out. If it's working, leave it alone.

If you calculate your time, money and get the Electrician out again, you have better luck leaving everything alone and just get another wire and run it down there. Save time, money and effort.

:thumbsup:
 

Tractor & Equipment Auctions

2019 CHEVY 5500 CAB CHASSIS (A50505)
2019 CHEVY 5500...
2015 INTERNATIONAL 4300 26 FT NON CDL BOX TRUCK (A51219)
2015 INTERNATIONAL...
2015 Ford F-150 Ext. Cab Pickup Truck (A50323)
2015 Ford F-150...
(INOP) VOLVO L70H WHEEL LOADER (A50459)
(INOP) VOLVO L70H...
Ford Super Duty 8ft. Truck Bed (A49346)
Ford Super Duty...
PENDING SELLER CONFIRMATIONS (A51219)
PENDING SELLER...
 
Top