That's locked rotor amps! What happens when you lock a rotor on a motor? You blow the breaker! It's not the same as starting amps.
Motor Calculations | NEC content from Electrical Construction and Maintenance (EC and M) Magazine
"
Motor locked-rotor current. If the rotating part of the motor winding becomes jammed so it can稚 rotate, no counter-electromotive force will be produced in the motor winding. This results in a decrease in conductor impedance to the point that it痴 effectively a short circuit. What痴 the result? The motor operates at locked-rotor current, often six times the full-load ampere rating, depending on the motor Code Letter rating [430.7(B)]. This will cause the motor winding to overheat and be destroyed if the current isn稚 quickly reduced or removed."
Electrical Motor Calculator
Plugging in 1 hp , 90% efficiency, 85 PF (power factor) and 230V to the calculator in this link.
You get:
1 phase = 4a.
FLA = 5A
What does FLA stand for? Full Load Amps! At full load the motor draws 5A, 230V * 5A = 1150W; 1 HP = 746W FLA for a 1 HP motor = 1150/746 or 1.54 times.
Now look at the chart for starting amps, what does the FLC state? 150% to 300% of running current and what's 300%? It's 3 times, exactly what I said. I work with this stuff everyday my systems are built on these calculations. Are you off the grid running several inverters on a daily basis?