Home AC Welder Breaker ???

   / Home AC Welder Breaker ??? #1  

Beltzington

Platinum Member
Joined
Oct 4, 2008
Messages
954
Location
Appling, Georgia
Tractor
JD 3720
According to the welders owners manuel I need a 50-Amp 230v breaker to run my new to me stick welder and I have an open single breaker space on my GE panel. I can buy a 50-amp dual throw breaker that will fit in this slot. My service is 200-amp and currently I am running <70% capicity with everything turned on, I would not run our 30-amp dryer while welding so I believe I would still be pulling less amps than capacity but would be close. My concern is possible feedback (amp surges or voltage spikes) that might damage the expensive electronics in my home. Is there something more I should do then just connect the outlet? TIA
 
   / Home AC Welder Breaker ??? #2  
How do you get 230 volts out of a single breaker slot?. You have to have connection to both legs of the entrance. and all the boxes I have seen alternate the legs in each slot as it goes down the box.. I am confused..
As for transients coming out of the welder, I have never killed anything in my house (Solid state modern Ham radio equipment , entertainment electronics etc)

James K0UA
 
   / Home AC Welder Breaker ??? #3  
I have had my Lincoln hooked up in a bunch of houses and shops and never did anymore than pop a 50amp breaker in the panel and let her rip,never had any issues. Good luck .
 
   / Home AC Welder Breaker ??? #4  
should be fine.

Welder shouldn't make any more spikes on the lines than the dryer or fridge turning on and off. But if you want to you could add a hole house surge supressor to the panel when you add the breaker.
 
   / Home AC Welder Breaker ??? #5  
How do you get 230 volts out of a single breaker slot?. You have to have connection to both legs of the entrance. and all the boxes I have seen alternate the legs in each slot as it goes down the box.. I am confused..
As for transients coming out of the welder, I have never killed anything in my house (Solid state modern Ham radio equipment , entertainment electronics etc)

James K0UA

I am going to guess he uses the slim style double throws that fit in the thicker slot....at least that's what I use in my garage.
 
   / Home AC Welder Breaker ??? #6  
But if using a double handled breaker that fits in a single space, 240 volts will not be what's coming out. A breaker of this type can give you two branch circuits, but they will both be on the same leg. This means that the welder will see 0 volts coming in as there will be no difference in potential between the two hot wires coming off the breaker.

What you want to do is put the welder on a two space two pole breaker which will provide the 240 volts you need. If necessary, use a double handled single space breaker to replace two 20 amp branch circuits to make the room in the breaker panel.

And don't worry about the welder creating spikes and whatnot. Lots of people have welders, some like me have several, and I haven't heard about anyone having the issues you are concerned about. My power company provides me with a lot more spikes and sags than my welders do.
 
   / Home AC Welder Breaker ??? #7  
How do you get 230 volts out of a single breaker slot?. You have to have connection to both legs of the entrance.

James K0UA

I was wondering the same thing?

I am also wondering what he means by "currently at 70% capacity"?

Cause a 200a service, if you are at 70% capacity, that means you are using 140a of power at a given time. That is unlikely or your electric bill would be astronomical.

But even so, 70% of 200 is 140. That leaves you 60a in reserve. You are only using a 50a. Whats the problem??

And if you do overdraw, thats what the 200a main breaker is for:thumbsup:
 
   / Home AC Welder Breaker ???
  • Thread Starter
#8  
But if using a double handled breaker that fits in a single space, 240 volts will not be what's coming out. A breaker of this type can give you two branch circuits, but they will both be on the same leg. This means that the welder will see 0 volts coming in as there will be no difference in potential between the two hot wires coming off the breaker.

What you want to do is put the welder on a two space two pole breaker which will provide the 240 volts you need. If necessary, use a double handled single space breaker to replace two 20 amp branch circuits to make the room in the breaker panel.

And don't worry about the welder creating spikes and whatnot. Lots of people have welders, some like me have several, and I haven't heard about anyone having the issues you are concerned about. My power company provides me with a lot more spikes and sags than my welders do.

Good Point - I was at the box store today and was looking at available c/b options, thanks for bringing this up, looks like I need to take a closer look at the bus bars. My AC and dryer both are running off the same side of the panel so I "assumed"....

I used a clamp on on amp meter before I built-on an addition which is why I know the current draw. I turned everything on which is obviously is not normal and was surprised curren was as low as it was.
 
   / Home AC Welder Breaker ??? #9  
Beltzington said:
My AC and dryer both are running off the same side of the panel so I "assumed"....

I think you are under the common misconception that one line is on one side of the panel, and the other line runs down the side. In fact both lines are on both sides. They alternate spaces. Both top spaces are on one line, the second space both sides are on the other line, and they alternate the whole way down. This is how you get 120 or 240 volts. Plug in a single space breaker and you grab one hot and then the circuit returns to neutral. Hot to neutral voltage is 120v. If you put in a two space breaker it grabs both lines, one on each of of the adjacent spaces. The circuit then runs from one hot to the other. Line to line voltage is 240v.

As far as approaching the capacity of your 200 amp service, take another current reading. This time just meter what it is on a typical day instead of metering it with everything running. My house usually pulls down less than 10 amps per leg to run the TV and whatever lights are on. Even if we were cooking thanksgiving dinner, doing laundry, and had every light and TV in the house going, I don't think it would get close to the 200 amps per leg that you can get through your main breaker before it pops.
 
   / Home AC Welder Breaker ??? #10  
Good Point - I was at the box store today and was looking at available c/b options, thanks for bringing this up, looks like I need to take a closer look at the bus bars. My AC and dryer both are running off the same side of the panel so I "assumed"....

I used a clamp on on amp meter before I built-on an addition which is why I know the current draw. I turned everything on which is obviously is not normal and was surprised curren was as low as it was.

When you open the box and look at it you will see only 1 connection point, and it will be 115 volts between this connection and the nuetral. You will have to have a 2 connection points in the back of the box and a double wide breaker to get across both legs. to get 230 volts. You will not be able to see it because you only have one space, but look at a box in the store and see how the legs alternate positions as they go down the box from the main breaker at the top. Like Lightndsound said you can get a double breaker (in a single slot) for two of your other circuits and move one of the single breakers out and put in a "double" single slot breaker to make room for a double breaker for 230 volts. Good luck..

James K0UA
 

Tractor & Equipment Auctions

2015 Jeep Cherokee SUV (A48082)
2015 Jeep Cherokee...
AUCTION STARTS HERE @ 9AM (A51242)
AUCTION STARTS...
Informational Lot - Financing (A51039)
Informational Lot...
UNUSED 3/4 in. Polyester Arborist Outdoor Rope (A50860)
UNUSED 3/4 in...
2016 Ottawa Yard Spotter Truck - Cummins Diesel, Allison Auto, Hydraulic Air Fifth Wheel, 33,000 ... (A51039)
2016 Ottawa Yard...
Kubota SVL95-2 High Flow Cab Skid Steer (A51039)
Kubota SVL95-2...
 
Top