New one to me on the CLOG never seen it... One that hit one of my old companies was the day shift Electrical Maintenance crew decided the Main Pump went bad. They were on phone calling well company (1000 bucks to pull the pump) We pumped well over 4 million gallon a month there with a 3 phase 50hp submersible pump set at an astounding 65 feet.! It ran off 480 3phase inverter with soft ramp up and a air over water bladder tank that was 20 some feet high and probably 14' across. That thing would push gravel size of marbles thru the lines
Anyhow they all yelling no water plant gonna have to have NEW pump put in (note it was only 4 months old pump as they said it went bad on same shift while prior.) Now me and my other 8hr 2nd shift electrician went to looking. Pulled voltage readings under the VFD and they were all over. Something not right for sure, maybe bad VFD so more looking on top side of BIG VFD Voltage all over... Ok lets head backwards. the issue ended up being a Bus Bar (Plug in Fused Disconnect) 200+ feet away. It had BURNT off the buss bar contact points, luckly we could move it backwards one point install a new one and back up and running... We had to CAN a un-used disconnect from different part of the plant but the wiring all worked out and had it back running in 2 or so hours. The other guys could have had a real reaming but we (other 8hr electrician and I) covered for them & said it was really hard to find... :/