Everything looks good in your latest picture, except a 'grounding electrode conductor' is required to a grounding electrode (e.g. ground rod).
One rod would be ok.
As per NEC 250.66: For a #10 feeder into the sub-panel, a #8 copper 'grounding electrode conductor' from the ground bus to the rod would be ok.
As per 250.53(G), if rod encounters a rock bottom, rod can be driven at an angle of up to 45 degrees, if this is not sufficient, rod can be buried horizontally at a 2 ft depth.
One rod would be ok.
As per NEC 250.66: For a #10 feeder into the sub-panel, a #8 copper 'grounding electrode conductor' from the ground bus to the rod would be ok.
As per 250.53(G), if rod encounters a rock bottom, rod can be driven at an angle of up to 45 degrees, if this is not sufficient, rod can be buried horizontally at a 2 ft depth.