Generator in a outside building and powering the panel...

   / Generator in a outside building and powering the panel... #81  
Can you site the code please? Thank you.

Howdy,
So even without citing code, you think its ok to send a live feed in both directions when on generator power?

So in real world use, the barn sub-panel will be energized while on generator, as you now have multiple neutral+ ground locations

Stop getting your panties in a bunch. He has existing conduit under the driveway, like I said before, just run the separate lines and proper interlock and be done.
 
   / Generator in a outside building and powering the panel... #82  
I don't understand the panties comment. I simply politely asked for the code site since you said it would be contrary to code.

If you really can't site the code that's OK just say so. If you can site it it would be good to know.
 
   / Generator in a outside building and powering the panel... #83  
Gpin, why bother. He is going with the cobb job no matter what he is told.
 
   / Generator in a outside building and powering the panel... #85  
What we have going on here is the layman's standards for electrical equipment and the NEC requirement's endorsed and used by professionals in the electrical field.
The pro understands the electrical theory why those silly rules are written and enforced by law. The layman figures if the equipment works without immediately exploding into a sparking ball of flames that the installation is satisfactory.

Site the code.
 
   / Generator in a outside building and powering the panel...
  • Thread Starter
#87  
Gpin, why bother. He is going with the cobb job no matter what he is told.
Riiiiight, that is why I am asking what code is, vs just going and doing it...
You claim to be an expert, cite some code to back up your assertions or explain why it is a bad idea.

Howdy,
So even without citing code, you think its ok to send a live feed in both directions when on generator power?
So in real world use, the barn sub-panel will be energized while on generator, as you now have multiple neutral+ ground locations
Can you explain a little what you mean? I am not quite following you. Yes, the barn subpanel will be hot while the generator is on. It feeds the barns where the critters are and the critters need to be kept from freezing...

Show me where it is against code and I will happily follow the code, this WILL be done right the first time.
But at the same time, I am not going to go and spend $500+ to get the same effect as I could for $40-150 (as buickanddeere suggested I do when he suggested that I install a Reliant interlock panel ahead of the current panel).

Aaron Z
 
   / Generator in a outside building and powering the panel... #88  
Howdy,
OK, your barn sub-panel is connected and working properly? OK, that means it has a master circuit breaker at the main service panel. That means all the wires are correct. You want to add a 50amp dual pole breaker with a interlock. OK but, you only want to use 2 wires. OK, in theory it sounds good, but when you switch over the interlock, (shuts off main, turns on generator breaker), the 2 wires are feeding the main panel, and the neutral and ground are still attached to the main service panel ground bar, and somehow connected to the sub-panel and generator. I understand what you want to do. It would be like saying use 2 separate 50 amp breakers, one at location 3 and the other at location 18 for your dual pole breakers. It's just not done.

Because of the limited draw at the barn sub-panel, because you have conduit in the ground, get the interlock for your panel, get you dual pole 50 breaker, and run 4 wires properly. Your not gonna break the bank with adding those 2 wires to a 100ft run. move on
 
   / Generator in a outside building and powering the panel... #89  
"It's just not done."

"... out of code for electricity flow" (whatever that means).

So you really don't have a site to offer. That's ok. No one else does either.
 
   / Generator in a outside building and powering the panel... #90  
"It's just not done."

"... out of code for electricity flow" (whatever that means).

So you really don't have a site to offer. That's ok. No one else does either.

700.19 Multiwire Branch Circuits Prohibited

A new 700.19 has been added addressing multiwire branch circuits used in emergency systems. This new provision prohibits multiwire branch circuits protected by common trip circuit breakers to serve emergency lighting and power circuits. Emergency lighting and power could be unavailable during ordinary line to ground faults and other problems where common trip circuit breakers or handle ties are employed. Continued reliability of emergency circuits requires this change. [ROP 13-118]
 

Tractor & Equipment Auctions

2018 Ford Explorer AWD SUV (A51694)
2018 Ford Explorer...
TRUCKING INFO (A50774)
TRUCKING INFO (A50774)
MM60 SERIES II QUICK ATTACH MULCHER (A51243)
MM60 SERIES II...
Parker 250 bu Gravity Wagon / Seed Tender (A50515)
Parker 250 bu...
HONDA FOURTRAX 300 FOUR WHEELER (A51243)
HONDA FOURTRAX 300...
2014 JLG G12-55A 12,000LB 4x4 Rough Terrain Telehandler (A50322)
2014 JLG G12-55A...
 
Top