What size service wire for new workshop

   / What size service wire for new workshop #1  

747driver

Veteran Member
Joined
Apr 17, 2010
Messages
1,220
Location
Tellico Plains,TN
Tractor
Kioti CK27 HST
I am running new electrical wire service for my barn from the house. The house is 200 amp service. The run to the barn is 120 ft. I have figured i will need #4 XHHW wire. This wire is made for running in conduit which i am doing, is more flexible also for pulling.

I have a 125 amp service panel at the barn. Does this #4 size wire work ? Will put a 60 amp breaker at the house and a 50 amp main breaker on the box at the barn ? I have a 220 tablesaw, 220 air compressor, 220 wood jointer as my big power draws.

Thanks

Chuck
 
   / What size service wire for new workshop #3  
Why a 50 amp in the burn and 60 at house. Should be the same size.
 
   / What size service wire for new workshop #4  
Why a 50 amp in the burn and 60 at house. Should be the same size.
Perhaps to avoid tripping the breaker in the house? Shorter walk to the barn/shop panelbox than to the house one.

Aaron Z
 
   / What size service wire for new workshop #5  
Voice of experience.... Save yourself the time and expense of doing it over later. Pull bigger wire now. I would pull enough to make a 200A subpanel, even if you don't use it to the fullest right now. Your power needs will only grow with time. Pull 2/0 copper or the alum equivalent (looks like 250 mcm, but don't quote me on that...).Later on you may find that you need more and want to upgrade your house service to accommodate that. If you pull big wire now, you will make your life easier later. If you (seriously) believe that you will not live here for the long term, then you will probably just want to do what you suggested.

My $0.02
 
   / What size service wire for new workshop #6  
I agree with Dave as I have learned the hard way that what you think is fine now will not be enough later.
 
   / What size service wire for new workshop #7  
Voice of experience.... Save yourself the time and expense of doing it over later. Pull bigger wire now. I would pull enough to make a 200A subpanel, even if you don't use it to the fullest right now. Your power needs will only grow with time. Pull 2/0 copper or the alum equivalent (looks like 250 mcm, but don't quote me on that...).Later on you may find that you need more and want to upgrade your house service to accommodate that. If you pull big wire now, you will make your life easier later. If you (seriously) believe that you will not live here for the long term, then you will probably just want to do what you suggested.

My $0.02

Put oversized conduit instead than pull the proper size wire you need now. If your needs change, you pull the existing cable out and replace it to your new needs. 2/0 cu is expensive for 120' if you'll never need it. Remember, only calculate the loads that will be used simultaneously.
 
   / What size service wire for new workshop #8  
One important thing you didn't tell us is are you planning on running copper or alum. wire ????

Wire Size Calculator
 
   / What size service wire for new workshop #9  
Put oversized conduit instead than pull the proper size wire you need now. If your needs change, you pull the existing cable out and replace it to your new needs. 2/0 cu is expensive for 120' if you'll never need it. Remember, only calculate the loads that will be used simultaneously.

I'll go one step further, when placing conduit from house to barn, put in another smaller conduit line at the same time to have for later. (Cat6, phone, coax, or fiber) think security systems, remote control for lights, cable or satellite TV, networked cameras, or even a intercom system from house to barn.
I have trenches from the house to the barn 3 times now, the last time I put in 2" pvc conduit, so when I decide I need something else out there, I have room in the conduit (and a pull string) so I can get it out there without having to dig again. There may always be something new you want to add, that you weren't thinking of 4 years ago. More of the learning things the hard way.
 
   / What size service wire for new workshop #10  
Agree that installing 2'' conduit is a good idea. #4 AL may be fine, depends on how much equipment runs simultaneously. I have an equipment shed fed with a 200' run of #4 AL. Biggest load is AC welder. Also have air compressor and lights. 60 amp breaker has never tripped in 10 years of use. The caveat is that it is almost always just one person doing anything in there. No need for copper in that conduit unless you have deep pockets and like spending it.
 

Tractor & Equipment Auctions

2013 John Deere 35D Mini Excavator (A49461)
2013 John Deere...
SOLDERING IRONS, GLOVES, AND STANDS (A50854)
SOLDERING IRONS...
Case 1150G Crawler Tractor Dozer (A50322)
Case 1150G Crawler...
12 FLATBED W/ 300GAL WATER TANK (A50854)
12 FLATBED W/...
UPDATED INTERNET BUYER'S PREMIUM TERMS (A50774)
UPDATED INTERNET...
2013 Ford Expedition 4x4 SUV (A49461)
2013 Ford...
 
Top