I have thought about that. I need to contact the electric company and see what the extra cost is.
Perhaps to avoid tripping the breaker in the house? Shorter walk to the barn/shop panelbox than to the house one.
Aaron Z
One important thing you didn't tell us is are you planning on running copper or alum. wire ????
Wire Size Calculator
Don't be scared to use aluminum feeders conductors. Use the proper paste and you'll be fine. As an electrician I just have started quoting aluminum as it seems everyone else has gone that way. The saving can be as much as %75 depending on the size and type.
Why a 50 amp in the burn and 60 at house. Should be the same size.
Voice of experience.... Save yourself the time and expense of doing it over later. Pull bigger wire now. I would pull enough to make a 200A subpanel, even if you don't use it to the fullest right now. Your power needs will only grow with time. Pull 2/0 copper or the alum equivalent (looks like 250 mcm, but don't quote me on that...).Later on you may find that you need more and want to upgrade your house service to accommodate that. If you pull big wire now, you will make your life easier later. If you (seriously) believe that you will not live here for the long term, then you will probably just want to do what you suggested.
My $0.02
Not by code here in Indiana. All sub panels must have a breaker 10 amps smaller so it trips at the sub 1st.
Chris