Going to be wiring my shop soon and am planning things out. We have no code or inspections to follow here but want to do it right.
Everything is going to be in conduit. But I want to minimize how much of it I use. So my first question
As I understand it, I can run 9 current carrying conductors in 1/2" emt correct? The layout I am planning, I need 4 circuits on my largest run of emt. That's 9 wires if I run 4 hot, 4 neutral, and a ground. But pulling 9 wires in 1/2 don't sound like fun.
I was considering a mwbc and only using 2 neutrals. My understanding is I can run 2/hots with 1/neutral as long as they are on different phases. But was wanting a way to distinguish between neutrals later down the road if I decide to splice in somewhere where a wire end is not visible. I want to make sure to keep the hots and neutrals balanced.
Like running a pair of black hots with a white neutral and a pair of reds with ?? Blue? Grey? Some other accepted color. So in the future if I decide to open up a tee or j-box I know I am grabbing the right pair as to not overload the neutral. Not to mention it will make it easier initially.
Everything is going to be in conduit. But I want to minimize how much of it I use. So my first question
As I understand it, I can run 9 current carrying conductors in 1/2" emt correct? The layout I am planning, I need 4 circuits on my largest run of emt. That's 9 wires if I run 4 hot, 4 neutral, and a ground. But pulling 9 wires in 1/2 don't sound like fun.
I was considering a mwbc and only using 2 neutrals. My understanding is I can run 2/hots with 1/neutral as long as they are on different phases. But was wanting a way to distinguish between neutrals later down the road if I decide to splice in somewhere where a wire end is not visible. I want to make sure to keep the hots and neutrals balanced.
Like running a pair of black hots with a white neutral and a pair of reds with ?? Blue? Grey? Some other accepted color. So in the future if I decide to open up a tee or j-box I know I am grabbing the right pair as to not overload the neutral. Not to mention it will make it easier initially.