Are you just trying to save money by running fewer wires or is there some reason you want to limit yourself to using the smallest sized conduit you can?
Eddie
Fewer wires to make it easier to pull 4 circuits worth through 1/2" EMT. I still plan on pulling a ground and not relying on conduit connections staying tight over the years. So, if I can get 4 circuits down to 7 wires instead of 9 and it will work just the same, is easier, and cheaper, why not.
The reason for 1/2" is because the standard single boxes I have only have knockouts for 1/2". Only the double boxes have a few 3/4" knockouts. I didnt want to have to go through several boxes making the knockouts bigger.
Since this is a shop, are you planning on using power tools? Are they all going to be 20 amp lines with 12 gauge wire?
Yep, mostly power tools. And yes, all 20a 12ga thhn/thwn wire
Is there a cost savings in only buying one color wire?
Eddie
Not really. I have spools and spools of wire already. I can use whatever I want
If you ran 12/3 romex, you wold have two hots for one neutral and a ground. I wouldn't change that ratio anymore then that.
Eddie
Exact same thing I want to do, only not romex. Just stranded wire. 2 hots (on different phases) for each neutral. But I want 2 of those circuits in the conduit, thus wanting a different color for the second neutral so I can keep track of what neutral belongs to what phases.
In my shop, I ran 12/2 for each circuit with my lights on a separate line.
Eddie
That would be the same as if I ran 4 neutrals to go with the 4 hots. But if the extra neutrals are not needed for anything, Why use extra material and make more work for myself.
First, I am a certified (master) electrician in Wisconsin. Here is an NEC pipe fill chart.
Conduit Fill Chart
The ground is not counted as it is not a current carrying conductor. You also have to consider the derating factor.
Electrician Testing- A guide for all Electricians: Wire Ampacity and Conduit Fill Calculation
This table shows that for (your case) you would have to derate 8 conductors in a raceway to 70 %.
If you did share the neutral with 2 hots you would have to have the hots on a 2 pole breaker. You have to be able to open the hots with a single switch handle (breaker).
Personally, I would use 3/4" or 1" conduit for the main runs. It leaves room for future expansion.
I have already seen the tables. De-rating doesnt apply per-say. The When the conductors are good for 30a, 70% derate is still 21a and adequately protected by a 20a breaker. Thus, I am allowed up to 9 CCC in conduit on a 12a breaker.
The two pole breaker is is something I havent seen mentioned yet though. I assume that is just a safety thing some someone doesnt get bit by the neutral that is tied to two breakers, and the unsuspecting person only killed one of the breakers?