I'm hooking up my outside boiler and the trenches are dug, but my question is what gauge of wire do I need? the OWB has 2 I want a cable with 3 so I can ground it to the frame.
 
   / under ground wire help #2  
That will depend on the draw of whatever you are powering. What does the rating plate say on the boiler?
 
   / under ground wire help #3  
My guesses:
Does it have a: Blower? (60-250 watts)
Solenoid for air? (10 watts)
A convenience light? (13-150 watts)
A receptacle (widely variably, call it 180 watts) That's a worst case of say 600 watts, which is 5 amps at 120 volts.
How far is boiler from panel?
For 5 amps a #12 gauge should be able to run a few hundred feet (others with can confirm) with under a 3% (3.6V) voltage drop.

You need to run a 3/c cable so that if your circuit ever shorts to the boiler, there's a low resistance path on the green wire back to the utility's transformer so that lots of current can short into the boiler and the breaker will trip.
 
   / under ground wire help #8  
Well then I'm good at 95'

Depends on the amp draw.

Wire size is based on 2 things. Length, and amps. You have only provided 1 part.
 
   / under ground wire help
  • Thread Starter
#9  
I'll go with #12 that should be good enough to run the pumps and the light.
 

Tractor & Equipment Auctions

2014 CHEVROLET IMPALA 4DOOR SEDAN (A54313)
2014 CHEVROLET...
2004 TerraGator 8104 (A55301)
2004 TerraGator...
NEW Woods 6ft Finish Mower (A55218)
NEW Woods 6ft...
2016 Ford Fusion SE AWD Sedan (A53424)
2016 Ford Fusion...
2019 Ford F-550 4x4 Ext. Cab Chipper Truck (A51692)
2019 Ford F-550...
2015 TROXEL 130BBL KILL TRAILER (A53843)
2015 TROXEL 130BBL...
 
Top