I'm hooking up my outside boiler and the trenches are dug, but my question is what gauge of wire do I need? the OWB has 2 I want a cable with 3 so I can ground it to the frame.
THis might help.
wire size calculator
That says #12 is good for 5 amps out to 205 feet and still keeps above 3% voltage drop.THis might help. wire size calculator
That says #12 is good for 5 amps out to 205 feet and still keeps above 3% voltage drop.
Well then I'm good at 95'
THis might help.
wire size calculator
I'll go with #12 that should be good enough to run the pumps and the light.
I'll go with #12 that should be good enough to run the pumps and the light.
I'll go with #12 that should be good enough to run the pumps and the light.
Or run the UF wire and your insulated piping all in the same 4" corrugated drain.I would run conduit and put your wire in that. Less chance of having to dig it back up after a rock nicks the wire that way.
Aaron Z
Or run the UF wire and your insulated piping all in the same 4" corrugated drain.