Electrical advice needed
   / Electrical advice needed #71
Yes, the spec sheet is messed up... most likely a misprint. I figure they meant to say 24 amp motor rating.
Take a look at that belt drive and see if yould really like to stick with that.
   / Electrical advice needed #72
This is the spec sheet for the equipment, why not follow it?
Electrical:
Power Requirement........................................................................................................... 220V, Single-Phase, 60 Hz
Prewired Voltage.................................................................................................................................................. 220V
Full-Load Current Rating........................................................................................................................................ 25A
Minimum Circuit Size.............................................................................................................................................. 30A
Connection Type....................................................................................................................................... Cord & Plug
Power Cord Included............................................................................................................................................... No
Recommended Power Cord............................................................................... 鉄?Type, 4-Wire, 10 AWG, 300 VAC
Recommended Plug Type................................................................................................................................. L15-30
Switch Type............................................................................................ Control Panel w/Magnetic Switch Protection
Is this for the OP's piece of equipment? I missed where he posted it if it is.
   / Electrical advice needed #73
Finding this whole conversation somewhat amusing...regardless of the site/board, when it comes to electricity the board "lights up". OP apparently has the manual for his tool. I would do what they say. I'm sure the manufacturer has "done the math" because of legal/warranty concerns. Can't hurt to oversize the circuit but why? Cost goes up as the size goes up.
YESSSSS!!!!!
But some (notably B&D) do know a LOT more than the equipment manufacturer. :stirthepot:
Maybe the 5hp "spec" is like the advertising for Harbor Freight and other Chinese motors/equipment, as in "develops UP TO 5hp" (given a big enough flywheel).
   / Electrical advice needed #74
I don't want to derail a thread, but have one question. I have a 1-1/2 HP table saw and can run on 120 ore 220. Any advantages on running 220? It is 110 right now and works fine.
   / Electrical advice needed #75
Will use less voltage.
   / Electrical advice needed #76
What?
You can run it off a smaller wire if 220, you won't get lights dimming, so much, when the motor kicks in and you may save abit of $$.
   / Electrical advice needed #77
You can use smaller wiring because it will pull half the amperage. But being a 1.5 HP motor, 120 isn't a problem.
It should pull about 15a if 120v and 7.5 a if 240v.
So it will run just fine on a standard 20a 120v circuit. And gives alot better mobility/portability. Just don't want to run a bunch of other crap on the 120circuit or you may deal with breaker trips.
   / Electrical advice needed #78
I found the info at this link thought the op had posted but was mistaken. May not be the same machine.
Shop our G8622 - Sliding Table Shaper at Grizzly.com
   / Electrical advice needed #79
What?
Sorry meant amps
   / Electrical advice needed #80
if the motor specs at 14FLA. Minimum ampacity of the cable is 17.5amp. Non delay fuses 45amp, tome delay fuses 25amp or a 30amp breaker.