A planer does not start under load, so locked rotor current of ~ 100A on a 30A motor would be extremely brief. A 30A double pole breaker may sustain that brief starting surge. ... AWG 10 copper will sustain your FLA running current fine, and if a short length run thats what Id use IF a 30A breaker is determined not to give nuisance trips on startup. Going to 40A and 8Ga would give plenty of wiggle room.Based on the information I have supplied, can you recommend a wire size and amperage for the breaker? That's all I am asking.
You need 3 wires -- 2 hots and Ground. A 4th wire will be needed only if your planer needs a neutral to run an auxiliary 120V circuit.