Breaker Size?

   / Breaker Size? #11  
How pray tell so you obtain a ground , neutral and two live lines from a three prong plug and receptacle ? Anyone advocating the use of a double male suicide cord and without a fail safe transfer switch. Their opinions should be ignored .

NEMA 14-50 is a 4 pin plug (hot, hot, neutral, ground).

And I did say a sucide cord wasn't a great idea.
 
   / Breaker Size? #12  
I wonder if that's a recent change? When I built my house in 2000 the electrician put in a 50 amp 3 wire in the garage for my welder.
Don't know when the code changed but when a hot tub service panel was added (50amp) in 1998, it was 3 wire. This was before our time in the house. Our hot tub died earlier this year and when I spoke with the shop about putting a new one in, the guy said how old was your tub... I told him and he said I'd better check if you have 3 or 4 wire.
 
   / Breaker Size? #13  
The breaker is to protect the wires to the outlet and should be sized accordingly.

Doug in SW IA
 
   / Breaker Size? #14  
The breaker is to protect the wires to the outlet and should be sized accordingly.

Doug in SW IA

Short circuit protection or thermal protection? It depends . Do you agree that a 90 amp breaker is acceptable on a 38 amp motor with #8 R75 copper .
 
   / Breaker Size? #15  
Short circuit protection or thermal protection? It depends . Do you agree that a 90 amp breaker is acceptable on a 38 amp motor with #8 R75 copper .

You will burn up that #8 wire, maybe cause a fire, long before the breaker will trip except for maybe a solid short circuit. There are motor rated breakers that will withstand the starting inrush w/o tripping unless the rotor locks up.

Ron
 
   / Breaker Size? #16  
Short circuit protection or thermal protection? It depends . Do you agree that a 90 amp breaker is acceptable on a 38 amp motor with #8 R75 copper .
Breakers & fuses protect wire from overheating & starting fires. They aren't there to protect devices plugged into ir connected to the wires. Sockets are considered part of the wiring in that aspect.
 
   / Breaker Size? #17  
You will burn up that #8 wire, maybe cause a fire, long before the breaker will trip except for maybe a solid short circuit. There are motor rated breakers that will withstand the starting inrush w/o tripping unless the rotor locks up.

Ron

You are not up to date on the electrical code . Perfectly legal and safe with 38GLA , #8 R75 wire and a 90 amp breaker . . Do you know the difference between thermal protection and short circuit protection ? Why would the wire burn up?
 
   / Breaker Size? #18  
For a random 50 amp wall receptacle use a 50 amp breaker and #8 R75.
From that 50 amp wall receptacle and 50 amp breaker it is legal to use #10 SOW Cab Tire cable rated for 30amps if the welders FLA is 24 amp.
 

Tractor & Equipment Auctions

2005 Nissan Titan (A50121)
2005 Nissan Titan...
2025 New/Unused Wolverine 72'' Skid Steer Ripper (A51573)
2025 New/Unused...
2017 John Deere Gator TS Utility Cart (A50324)
2017 John Deere...
Toro Workman 175 Sprayer Cart (A50324)
Toro Workman 175...
2002 Genie S-125 4x4 125ft Telescopic Boom Lift (A52377)
2002 Genie S-125...
New/Unused CFG Industrial H15R Mini Excavator (A51573)
New/Unused CFG...
 
Top