Those who add up watts will be bitten in the backside with VAR’s and wonder why the 4800 watt load keeps tripping the breaker on the 5000 watt generator .

correct.. you can't simply add them up, but they are still inter-related.

Most people don't understand motor start loads either, and why some air handler / compressor systems have a delay built in to stagger starting loads.
 
   / PTO Generator on 1920 Diesel,,,, #13  
Fuel consumption depends on generator load About 1.5 TO 2.5 GPH.
 
   / PTO Generator on 1920 Diesel,,,, #14  
Fuel consumption depends on generator load About 1.5 TO 2.5 GPH.

I would hope that your little Ford wouldn't use that much fuel on a small generator, it will vary with the load but you should be under a gallon/hour. My generator is a 25 KW but under normal use I average about a gallon / hour with either 80 HP or 65 HP on it, I do run the big one in the economy pto speed.
 
   / PTO Generator on 1920 Diesel,,,, #15  
I would hope that your little Ford wouldn't use that much fuel on a small generator, it will vary with the load but you should be under a gallon/hour. My generator is a 25 KW but under normal use I average about a gallon / hour with either 80 HP or 65 HP on it, I do run the big one in the economy pto speed.

Bottom line, fuel usage is based on generator electrical load.. can't dodge physics. there is a certain amount of energy in the fuel, and there is a physical conversion from hp to wattage.

No free meals.
 

Tractor & Equipment Auctions

2017 Chevrolet Silverado 1500 Crew Cab Pickup Truck (A55973)
2017 Chevrolet...
UNUSED FUTURE HYD HEDGE TRIMMER (A52706)
UNUSED FUTURE HYD...
401 (A52706)
401 (A52706)
2014 INTERNATIONAL  DURASTAR 26FT BOX TRUCK (A58017)
2014 INTERNATIONAL...
2016 CATERPILLAR 262D SKID STEER (A52709)
2016 CATERPILLAR...
Kubota SVL75-2 (A57148)
Kubota SVL75-2...
 
Top