We inherited my in-laws home that has a natural gas water heater that has a power vent (that I assume that pulls fumes out of the combustion chamber before the burner ignites).. the burner does not stay lit

The power vent comes on and off every 5 to 10 minutes and will run for 2 to 3 minutes each time.. it does this all the time, no matter if we have used (or are using) hot water or not.. I dont see how the water would cool down enough to trigger the heating cycle within this short time..

Is this power vent operation normal or something that I need a plumber to check out?

brian
 
   / Gas water heater power vent #2  
I'm guessing the burner is cycling?
 
   / Gas water heater power vent #3  
If the burner is cycling that often, then it needs adjusting.
 
   / Gas water heater power vent #4  
What kind of water heater is this?
Tank type or tankless?
What is this power vent?

I have a high efficiency Ream tank type.
It has a electronic butterly at the top of the tank before the flue to hold the heat in when it is not running.
 
Last edited:
   / Gas water heater power vent #5  
The higher efficiency gas appliances have lower stack temps and to ensure the all is vented properly a small blower is required.

I see it more on gas furnaces.

If the blower doesn't function the or at least if the sensor doesn't see a functioning blower the gas valve for the burner will not open.
 
   / Gas water heater power vent #6  
The higher efficiency gas appliances have lower stack temps and to ensure the all is vented properly a small blower is required.

I see it more on gas furnaces.

If the blower doesn't function the or at least if the sensor doesn't see a functioning blower the gas valve for the burner will not open.

Right, my furnace (PRO[ANE) is that way, vents through pvc high effiency, 1991 era.
Had a problem with it lighting then shutting off blower, it would keep running then relight...primary and secondary fans kept running,
It was the flame sensor, pulled out, cleaned with scotchbrite
2 years good now
 
   / Gas water heater power vent #7  
Sounds like the air flow proving switch isn't working. there should be a diaphragm switch with a small piece of flexible tubing going over to the stack. Pull the tubing off the stack and then suck/blow on it and you should hear the switch click on and off. If you don't it's not functioning properly. The burner goes through a set sequence for firing. Purge, which runs the blower to evacuate any flammable concentrations of gas in the combustion chamber. Main flame trial for ignition and then a post purge after the burner shuts off.
 
   / Gas water heater power vent
  • Thread Starter
#8  
couple things i noticed - it does not cylce on/off at night..

this is a tank (50 gal-ish i guess) natural gas unit.. with on demand ignition (no pilot light)

ill go down this morning and get more info..

thanks for the ideas so far

brian
 
   / Gas water heater power vent #9  
My bradford powervent only comes on when its being used during the day. Perhaps your setting is a little too high.
These new hot water power vents is the way to the future and i love it due to fact you have more places to put it without worrying where chimney is.
 
   / Gas water heater power vent #10  
Yes... the only draw back is no electricity... no hot water
 

Tractor & Equipment Auctions

AMCO F42B-3626CS 13ft Pull-Behind Wheel Offset Harrow Tiller (A49461)
AMCO F42B-3626CS...
2005 Ford F-150 Ext. Cab Pickup Truck (A50323)
2005 Ford F-150...
2015 CATERPILLAR 289D SKID STEER (A51242)
2015 CATERPILLAR...
2010 LACROSSE LUXURY LITE TOURING EDITION TRAVEL TRAILER (A50854)
2010 LACROSSE...
2012 FREIGHTLINER CASCADIA (A50854)
2012 FREIGHTLINER...
2009 MACK CXU613 DAYCAB (A50854)
2009 MACK CXU613...
 
Top