Your last generator Maintenance Run

   / Your last generator Maintenance Run #3,751  
Check for voltage at the AVR sensing terminals if it has separate power supply and sensing inputs. Sounds like the regulator is not seeing output voltage and trying to compensate.
I agree, if it's not the AVR, it's probably the sensing input to the AVR.

Aaron Z
 
   / Your last generator Maintenance Run #3,752  
On Sunday, I was out with my brother and dad building the new greenhouse. At around 10 the generator started for its weekly run. Normally it is a smooth instant start, but this time is turned over for several seconds and wouldn't hold a smooth rpm for another 10 or so seconds. Went to check it out, and noticed the temp gauge wasn't even registering (<100F). Turns out, after 10 years, the coolant heater must have died (shorted) in the last week sometime (popped the GFCI). Ordered a new HotStart 1000W 120-140F and installed yesterday. Working like a charm after fixing a few leaks from the dry rotted hoses.
 
   / Your last generator Maintenance Run #3,753  
Check for voltage at the AVR sensing terminals if it has separate power supply and sensing inputs. Sounds like the regulator is not seeing output voltage and trying to compensate.

Thank you both (Aaron Z) for the info.
This is probably out of my league, but in the diagram below do I check for voltage on #2 and #6 wires?
Of note, I did find a bad crimp on one of those wires where it connects to the regulator. The connector was repaired though.
I IMG_2985.JPG
 
   / Your last generator Maintenance Run #3,754  
Thank you both (Aaron Z) for the info.
This is probably out of my league, but in the diagram below do I check for voltage on #2 and #6 wires?
Of note, I did find a bad crimp on one of those wires where it connects to the regulator. The connector was repaired though.
IView attachment 640546
Yes, check 2&6. I would also check 1&4.
As I read the schematic, 2&6 are the sensing input to the AVR to tell it how many volts it's putting out.
1&4 are the AVR output to feed into the rotor (via the brushes) and control the voltage of the field that 2&6 are driven off of.

Aaron Z
 
   / Your last generator Maintenance Run #3,755  
The various generator stories told, is why I opt to not have my generators run automatically, even though they could. I like to start them, listen to them and make sure there isn't a mouse nest in there or something. If they don't start, I was there and have a much better idea what happened, rather than just a diagnostic light or message. Trouble always comes out of nowhere it seems.
 
   / Your last generator Maintenance Run #3,756  
You should always be there to monitor the unit even if it’s an auto exercise. You will be able to track changes in starting, noises, instability and fix the root cause before it progresses to the point of failure and possible other damage.

I’ve spent over 20 years trying to convince people of this. Nobody thinks it important until it doesn’t work and they are on the 30th floor with no power to take the elevator to P3 where the generator is buried.
 
   / Your last generator Maintenance Run #3,757  
My Generac exl7000 just failed after 18 years :(
Having done monthly exercise at close to 50% load religiously, regular oil changes, and sheltered from weather, I am disappointed. It's putting out 170v on the 120v outlets and 340v on the 240v plug. Took out several surge protectors and an HVAC transformer.

I agree with the high load / low duty cycle comments about non commercial generators, which is why I got the 7k. Replaced with a Winco 15kw PTO generator, which now powers one complete panel.

Simple swap out of the failed AVR and check the wiring to the AVR.
 
   / Your last generator Maintenance Run #3,758  
On Sunday, I was out with my brother and dad building the new greenhouse. At around 10 the generator started for its weekly run. Normally it is a smooth instant start, but this time is turned over for several seconds and wouldn't hold a smooth rpm for another 10 or so seconds. Went to check it out, and noticed the temp gauge wasn't even registering (<100F). Turns out, after 10 years, the coolant heater must have died (shorted) in the last week sometime (popped the GFCI). Ordered a new HotStart 1000W 120-140F and installed yesterday. Working like a charm after fixing a few leaks from the dry rotted hoses.

Good Catch
 
   / Your last generator Maintenance Run #3,759  
Sometimes I am made aware of something, by sound, like dropping something, without knowing, and I realize how disadvantaged a person wih impaired hearing would be. Or you hear a retaining clip land on the far side of the shop AND have a good idea where to look.
 
   / Your last generator Maintenance Run
  • Thread Starter
#3,760  
On Sunday, I was out with my brother and dad building the new greenhouse. At around 10 the generator started for its weekly run. Normally it is a smooth instant start, but this time is turned over for several seconds and wouldn't hold a smooth rpm for another 10 or so seconds. Went to check it out, and noticed the temp gauge wasn't even registering (<100F). Turns out, after 10 years, the coolant heater must have died (shorted) in the last week sometime (popped the GFCI). Ordered a new HotStart 1000W 120-140F and installed yesterday. Working like a charm after fixing a few leaks from the dry rotted hoses.

The more Training done in Peace...... :thumbsup:

Not familiar with your particular dzl, but at what I'd expect for "cold" your way, 10 seconds seems a bit long...... filters done lately ?

Rgds, D.
 

Tractor & Equipment Auctions

KUBOTA M6800 UTILITY SPECIAL TRACTOR (A51406)
KUBOTA M6800...
2011 Chevrolet Camaro Convertible Coupe (A52377)
2011 Chevrolet...
2022 Club Car Tempo Cart (A51694)
2022 Club Car...
2018 John Deere TX Gator (A50123)
2018 John Deere TX...
New Holland C345 (A50123)
New Holland C345...
NEW HOLLAND 706 30 INCH 3PT DIRT SCOOP (A53473)
NEW HOLLAND 706 30...
 
Top