CH4Ohio
Veteran Member
You really need to check with the local gas company to be sure you know what their delivery pressure is. You might even want to get one of their servicepeople or service supervisors to take a look at a sketch of your house piping and size it for you.
As mentioned above, 7" w.c. is a typical delivery pressure, BUT it's also VERY common for the gas company to deliver 2# (2 pounds) of pressure when the house piping will be run with CSST (Corrugated Stainless Steel Tubing). (That's the yellow tubing you referred to.) The reason for this is that CSST is measured OD instead of ID, it's expensive, the fittings are expensive, and the corrugations add some restriction. So in order to be able to run a SMALLER size in CSST (as opposed to black iron pipe), the delivery pressure is increased. Lots of new subdivisions are entirely 2# (PSIG) delivery now for this reason.
Also, you mentioned that "manifold" in the attic. If you're talking about the actual manifold where you'll run all your CSST branch lines to feed from, you're going to want to put that someplace more accessible. Otherwise a residential piping system wouldn't really have a "manifold". You have a main line and then branch off of that with drops (tees) as needed.
The installation requirements for CSST are defined in the manufacturers installation instructions in detail. The National Fuel Gas Code, NFPA-54 also has requirements for every material.
With CSST you have to install protective strike-plates where it penetrates framing, etc. You need to clearly understand both and be sure you know what pressure your gas company is going to deliver before you'll know how to size it. Most everywhere you have to be "certified" to run CSST. What "certified" means varies by locale.
If you're just wanting to pipe with black iron, you might be able to do the work. Here where I'm at the gas company would just inspect visually (before it's covered) and do a final pressure check. You wouldn't even need a plumber if you're doing it on your own home. This varies by locale and gas company too.
Find out what they plan to deliver. If it's 7" w.c., you'll be surprised how much pressure drop a 60' run of 1/2" pipe will take. The entire system is supposed to be sized so that you reach each appliance with only 0.5" w.c. pressure drop. That's not 0.5" drop for each branch or pipe segment -- that's total from the meter to the farthest appliance. That's by the book.
These sizing tables are readily available -- just be sure you're looking at the heading on the table and it reflects the correct delivery pressure, pressure drop, specific gravity for natural gas, and pipe material.
Sounds like there's no question that you can install the pipe. But the last thing you want is for the visual or final inspection to turn you down because it's undersized and doesn't meet the code. Getting the gas company to consult and advise up front might eliminate any surprises later.
Just some items to consider . . .
Sorry to go on . . . but I just saw mention of your generator -- lots of generators REQUIRE 11" - 14" w.c. inlet pressure at their burner manifold even for natural gas. Another reason to see what the delivery pressure is and let the gas company know that you likely need a higher delivery pressure. The addition of a generator usually results in a larger meter too so they'll want to know the details of your total connected load. They'll usually send someone out to consult with you at no charge.
As mentioned above, 7" w.c. is a typical delivery pressure, BUT it's also VERY common for the gas company to deliver 2# (2 pounds) of pressure when the house piping will be run with CSST (Corrugated Stainless Steel Tubing). (That's the yellow tubing you referred to.) The reason for this is that CSST is measured OD instead of ID, it's expensive, the fittings are expensive, and the corrugations add some restriction. So in order to be able to run a SMALLER size in CSST (as opposed to black iron pipe), the delivery pressure is increased. Lots of new subdivisions are entirely 2# (PSIG) delivery now for this reason.
Also, you mentioned that "manifold" in the attic. If you're talking about the actual manifold where you'll run all your CSST branch lines to feed from, you're going to want to put that someplace more accessible. Otherwise a residential piping system wouldn't really have a "manifold". You have a main line and then branch off of that with drops (tees) as needed.
The installation requirements for CSST are defined in the manufacturers installation instructions in detail. The National Fuel Gas Code, NFPA-54 also has requirements for every material.
With CSST you have to install protective strike-plates where it penetrates framing, etc. You need to clearly understand both and be sure you know what pressure your gas company is going to deliver before you'll know how to size it. Most everywhere you have to be "certified" to run CSST. What "certified" means varies by locale.
If you're just wanting to pipe with black iron, you might be able to do the work. Here where I'm at the gas company would just inspect visually (before it's covered) and do a final pressure check. You wouldn't even need a plumber if you're doing it on your own home. This varies by locale and gas company too.
Find out what they plan to deliver. If it's 7" w.c., you'll be surprised how much pressure drop a 60' run of 1/2" pipe will take. The entire system is supposed to be sized so that you reach each appliance with only 0.5" w.c. pressure drop. That's not 0.5" drop for each branch or pipe segment -- that's total from the meter to the farthest appliance. That's by the book.
These sizing tables are readily available -- just be sure you're looking at the heading on the table and it reflects the correct delivery pressure, pressure drop, specific gravity for natural gas, and pipe material.
Sounds like there's no question that you can install the pipe. But the last thing you want is for the visual or final inspection to turn you down because it's undersized and doesn't meet the code. Getting the gas company to consult and advise up front might eliminate any surprises later.
Just some items to consider . . .
Sorry to go on . . . but I just saw mention of your generator -- lots of generators REQUIRE 11" - 14" w.c. inlet pressure at their burner manifold even for natural gas. Another reason to see what the delivery pressure is and let the gas company know that you likely need a higher delivery pressure. The addition of a generator usually results in a larger meter too so they'll want to know the details of your total connected load. They'll usually send someone out to consult with you at no charge.